Suprima 30 running by itself

Discussion in 'Plumbing and Central Heating' started by blushy, 9 Dec 2015.

  1. blushy

    blushy

    Joined:
    25 Nov 2005
    Messages:
    19
    Thanks Received:
    0
    Location:
    Kent
    Country:
    United Kingdom
    Just come home from work to find my house really really hot and found the boiler to be running when the heating controls (Potterton EP2) were on standby and the stat for the room temp was not lit up as in heating and water off.

    The heating timer went off at 8am like normal and the heating and hot water are off all day and come on at 3pm but I came home at 2pm to the hot house!

    I turned off the common mains electricity supply to the boiler as the heat was just too much.

    So now I don't know whether to suspect the timer, boiler, stat or 3 way valve! Any ideas?
     
  2. Sponsored Links
  3. ollski

    ollski

    Joined:
    8 Oct 2003
    Messages:
    7,090
    Thanks Received:
    543
    Location:
    Bristol
    Country:
    United Kingdom
    timer - likely, stat - no, boiler - unlikely, 3 port valve - possible, 2 x 2 port valves - very likely. 100 minutes with a multimeter will give you the solution.
     
    • Thanks Thanks x 1
  4. blushy

    blushy

    Joined:
    25 Nov 2005
    Messages:
    19
    Thanks Received:
    0
    Location:
    Kent
    Country:
    United Kingdom
    From the FAQ is my best bet is to check the voltage on the Orange wire in the airing cupboard where the valve and pump meet? 240v=sticking valve 50-150v something else.

    No 2x2 port valve, just a 3 port.
     
  5. ollski

    ollski

    Joined:
    8 Oct 2003
    Messages:
    7,090
    Thanks Received:
    543
    Location:
    Bristol
    Country:
    United Kingdom
    If it's an older acl lifestyle actuator I've had a lot of these fail to turn off as the heat causes the big solder blobs to expand on the actuator pcb and grey and orange touch causing demand. The newer ones are redesigned.
     
    • Thanks Thanks x 1
  6. geoff@cetltd

    geoff@cetltd

    Joined:
    5 Apr 2006
    Messages:
    1,076
    Thanks Received:
    11
    Country:
    United Kingdom
    Is there a perm. live feed to the switched live?
    have the relay contacts in the timer / stat welded themselves in the normally open position?
     
    • Thanks Thanks x 1
  7. blushy

    blushy

    Joined:
    25 Nov 2005
    Messages:
    19
    Thanks Received:
    0
    Location:
    Kent
    Country:
    United Kingdom
    The boiler hasn't malfunctioned since it did it initially but when the boiler is operating now it seems to make a high pitched noise similar to a kettle. Seems to do it more on the CH than the HW, any ideas please??
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom