TURBOmax VUW 242/1 E boiler problem

Discussion in 'Plumbing and Central Heating' started by stevepbuk, 4 Apr 2013.

  1. stevepbuk

    stevepbuk

    Joined:
    13 Mar 2010
    Messages:
    78
    Thanks Received:
    0
    Location:
    Tyne and Wear
    Country:
    United Kingdom
    Hi,

    I have a TURBOmax VUW 242/1 E boiler and recently we have had a few issues with the pressure gauge not working as expected. I looked at the gauge last week and it indicated a really low pressure ( around 0.5 ). I presumed it may be with me bleeding a few radiators which hadn't been turned on for a while and I therefore increased it to 1.5. About half an hour later there was water coming out of the back of the boiler ( the overflow is into the garage so I suspect it was coming from here ). The pressure was showing at 2.5 at the time. I therefore dropped the pressure down to 1.5 and all seemed well again.

    The following morning when I got up the pressure was back down to 0.3. However, the boiler still fired up and has worked fine ever since. Its is switched on for 14 hours a day and when I check the pressure intermittently throughout the day its always the same at 1.5 but it always drops back down to 0.3 when not being used.

    The only other information that is relevant is that British Gas changed the pressure gauge November last year because they said it was faulty.

    Any ideas of what is going on.

    Thanks

    Steve
     
  2. Sponsored Links
  3. lukejames

    lukejames

    Joined:
    2 Nov 2009
    Messages:
    190
    Thanks Received:
    8
    Location:
    Coventry
    Country:
    United Kingdom
    Could be your filling loop is not turned off fully or your expansion vessel is depleted & needs recharging.
     
    • Thanks Thanks x 1
  4. stevepbuk

    stevepbuk

    Joined:
    13 Mar 2010
    Messages:
    78
    Thanks Received:
    0
    Location:
    Tyne and Wear
    Country:
    United Kingdom
    Thanks.

    I have checked the Filling Loop and its definitely turned off. Is it likely that the expansion vessel is broken or would the pressure keep increasing if this was the case.

    Cheers

    Steve
     
  5. easyflow

    easyflow

    Joined:
    12 Jan 2008
    Messages:
    472
    Thanks Received:
    60
    Country:
    United Kingdom
    push the valve in on the ex vessel, if water comes out you need a new one.
     
    • Thanks Thanks x 1
  6. lukejames

    lukejames

    Joined:
    2 Nov 2009
    Messages:
    190
    Thanks Received:
    8
    Location:
    Coventry
    Country:
    United Kingdom
    You need to re pressurize the vessel. Have a look in FAQ at the top of the forum.
     
    • Thanks Thanks x 1
  7. stevepbuk

    stevepbuk

    Joined:
    13 Mar 2010
    Messages:
    78
    Thanks Received:
    0
    Location:
    Tyne and Wear
    Country:
    United Kingdom
    Ok will do. Thanks again.

    Steve
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom