Uncontrollable heating !

Discussion in 'Plumbing and Central Heating' started by puguser191, 26 Apr 2012.

  1. puguser191

    puguser191

    Joined:
    26 Apr 2012
    Messages:
    1
    Thanks Received:
    0
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Hello all - and HELP please :confused:

    I have a problem with my central heating now that the days are getting warmer- typical....

    I have a pumped s plan system with separate room stat.

    The problem is that my room stat is down at minimum, and the controller is currently on its 'off' cycle (ie not due to come on due to the timer) both demand lights on the tempus 6 timer are off (red lights not showing) yet my boiler is steady at 75 deg and all the radiators are hot (or feeds to the individual rad valves are)

    Any idea what might be causing this- I imagine the CH valve must be stuck open to allow circulation ??? but why is the boiler staying on?

    Thanks in advance
     
  2. Sponsored Links
  3. Doc955

    Doc955

    Joined:
    29 Jun 2006
    Messages:
    49
    Thanks Received:
    1
    Country:
    United Kingdom
    If the CH zone valve is jammed in the open position, it will be calling for heat from the boiler as the 'call for heat' signal comes from a microswitch activated by the valve's motion.
     
  4. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page