Discussion in 'Electrics UK' started by thepprentice, 23 Jun 2008.

  1. thepprentice

    thepprentice

    Joined:
    22 Oct 2007
    Messages:
    31
    Thanks Received:
    0
    Country:
    United Kingdom
    In an new commercial install, we are planning on using an existing swa fed from the main supply to feed one half of the building. This cable was made in 1988, would you see any issue in using this cable. It gives a insulation resistance of around 300Mohms. I am just wary of the age of the insulation breaking down in the near future.
     
  2. holmslaw

    holmslaw

    Joined:
    12 Dec 2006
    Messages:
    5,841
    Thanks Received:
    400
    Country:
    United Kingdom
  3. Sponsored Links
  4. SparkyMarky

    SparkyMarky

    Joined:
    4 May 2006
    Messages:
    135
    Thanks Received:
    1
    Country:
    United Kingdom
    Also depends on what you priced for. If you were working on one of my contracts for a new install, and re-used old cable or equipment without prior agreement then I wouldn't be best pleased. You'd be told to rip it all out and do the work again, and you'd probably also be crossed off the list as far as future work was concerned...
     
  5. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,591
    Thanks Received:
    377
    Country:
    United Kingdom
    I presume this cable is already in place? ultimately this is a descision that should be made by the customer, do they want a full rewire now or are they ok with you reusing existing bits that are still in appropriate condition.
     
  6. Sponsored Links
  7. industryspark

    industryspark

    Joined:
    8 Jul 2006
    Messages:
    704
    Thanks Received:
    11
    Location:
    Yorkshire
    Country:
    United Kingdom
    aside from the points already made about if the customer has asked for it to be ripped out i think you need to make a judgment.

    you state the IR's between conductors are above 300M ohms which i would consider as excellent readings. also what are the cable like visually? junks missing anywhere? glanded ok? any signs of rusting on the armour?

    all things you should be considering when assessing whether its fit for use. the factory where i work has many swa cables probably older than what you have running submains ect. when i work on the circuits i simply cant justify replacement of the cable on age alone. replacement of some of these cables would cost thousands of pounds and would be an absolute nightmare to run in. i prefer a process of regular testing and inspecting to assess condition and replace if i think its required.

    why not contact manufacturers if they are still going, they may offer advice, they may not. but 20 year old cable may still be perfectly fine to leave in place, just depends how hard a life its had.
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page