Vokera linea 24

Joined
4 Aug 2007
Messages
21
Reaction score
0
Location
Ayrshire
Country
United Kingdom
This boiler keeps losing pressure. on inspection i noticed the blow off is dripping constantly. At first i tried to check the expansion vessel, the valve would not let air in or out though. Need some help with what needs done guys :rolleyes:
 
Sponsored Links
Joined
2 Mar 2007
Messages
3,440
Reaction score
69
Location
Lancashire
Country
United Kingdom
Replace PRV, re-charge/ replace EV.

Look into some training with boiler manufacturers, alot of boilers have simular makeup (like cars, four wheels engines and so on), once you pick up the way they start up and run, then your away.

Or you could ring the tech lines whilst at the boiler, every bit helps.
I know what its like to come from a commercial background, but it aint rocket science ;) (unless its the new condencing rocket :LOL: ;) )
 

DP

Joined
10 Dec 2003
Messages
15,546
Reaction score
3,497
Location
Glasgow
Country
United Kingdom
At what pressure does PRV drip? Is the pressure gauge working?
 
Joined
23 Feb 2007
Messages
21,178
Reaction score
1,936
Location
Norfolk
Country
United Kingdom
Alfies Revenge said:
the blow off is dripping constantly.

I have this problem as well. Other halfs always complaining about washing my boxers. :LOL:
 