What size Earth Bonding Cable should be used in the kitchen, from tap to tap on the pips and on to the stainless steel sink? And can it be connected to the nearest earth on a socket or should it go to the CU that’s about six metres away from the sink in the next room?
 
Sponsored Links

mst

Joined
26 Nov 2006
Messages
327
Reaction score
0
Country
United Kingdom
you dont need to bond the sink at all.
 
Joined
18 Dec 2005
Messages
57
Reaction score
0
Country
United Kingdom
but if you want to 4mm is fine between pipes and sink
no need to go to cu
 
Joined
3 Jan 2007
Messages
65
Reaction score
1
Location
Hampshire
Country
United Kingdom
The reason I ask is because at the moment what looks like an old 6mm cooker supply cable from the CU . At the end of the cable near the kitchen sink under the floor broads is a choc block that is attached. To that is a 2,5mm cable that I have found to go up a pipe in the wall that ends up in the loft .The cable in the loft goes to a dead end at adjunction box and no where else. Going back to the choc block near the sink where the 2.5mm is connected there is also a bonding cable that’s attached to the block .The bonding cable goes from the block and than is connected to the sink pipes and not to the sink. . Has someone got any comments on this?
 
Joined
29 Sep 2003
Messages
2,844
Reaction score
68
Location
West Midlands
Country
United Kingdom
Welstead said:
Has someone got any comments on this?

Yes. It's an ignorant bodge-up.

Isolate (if possible remove) the redundant cable (all of it) and forget about the bonding.
 
Joined
11 Jan 2004
Messages
38,422
Reaction score
1,796
Country
United Kingdom
TANNERS said:
but if you want to 4mm is fine between pipes and sink
no need to go to cu

You don't "want to", because it is no longer recognised by the regs.

Supplementary may be fitted in commercial kitchens if the designer deems it necessary, but in dom kits it has now been decided against.

One of the reasons is that it can create parallel earth paths & can actually make the installation more dangerous rather than safer.
 
Joined
2 Jun 2005
Messages
14,841
Reaction score
477
Location
Cumbria
Country
United Kingdom
Welstead, does your water main come into the house in the kitchen? Is your pipework in metal?
If metal pipework is used, wherever it enters it should have a main equipotential bond. There is some info in the wiki re main equipotential bonding.
 
Sponsored Links
Joined
3 Jan 2007
Messages
65
Reaction score
1
Location
Hampshire
Country
United Kingdom
I’m in a bungalow and the main water comes in the bathroom and has a stopcock there, and it has main bonding on the copper pipe just before the stopcock. The CU is just the other side of the wall in the hallway. The pipes in the kitchen are copper. Will I still need to bond them?
 
Joined
31 Mar 2006
Messages
19,999
Reaction score
1,381
Location
Leeds
Country
United Kingdom
No you should not bond the pipes in your kitchen

I think Spark123 was just doulble checking that you didn't mis interpret the advice, and end up without a main bond to to your incomming water service.
 
Joined
18 Dec 2005
Messages
57
Reaction score
0
Country
United Kingdom
securespark said:
TANNERS said:
but if you want to 4mm is fine between pipes and sink
no need to go to cu

You don't "want to", because it is no longer recognised by the regs.

Supplementary may be fitted in commercial kitchens if the designer deems it necessary, but in dom kits it has now been decided against.

One of the reasons is that it can create parallel earth paths & can actually make the installation more dangerous rather than safer.

by whom
 
Joined
31 Mar 2006
Messages
19,999
Reaction score
1,381
Location
Leeds
Country
United Kingdom
As the regulation has been abolished, there is no reg number or page number.
 