It is a Y plan, one set of valve wiring and its got a white wire in it as one of the 5 wires.
 
Sponsored Links
Joined
22 Aug 2014
Messages
20
Reaction score
0
Location
Wiltshire
Country
United Kingdom
I'll double check tonight that it's got 4/5 wires coming from the valve into the wiring centre to confirm Y plan.

I'm assuming that if it's Y plan I still set up as per my diagram and there won't be an extra wire for HW OFF going to my programmer. (If there is should I just connect to the L)

upload_2016-12-6_14-49-15.png
 
Joined
20 Jul 2005
Messages
7,031
Reaction score
1,741
Location
Nottinghamshire
Country
United Kingdom
For 'Y Plan' with a single 3 port motorised valve, there should be a wire from the 'HW off' on your existing programmer that goes to the Grey wire on the motorised valve.

That will connect to the 'hot water satisfied' on the Heatlink
 
Sponsored Links
Joined
18 Oct 2007
Messages
10,587
Reaction score
1,352
Location
Kent
Country
United Kingdom
For 'Y Plan' with a single 3 port motorised valve, there should be a wire from the 'HW off' on your existing programmer that goes to the Grey wire on the motorised valve.

That will connect to the 'hot water satisfied' on the Heatlink

A wire from cylinder stat Sat terminal must also be connected to the grey wire/HW Sat, i.e. three wires connected together.
 
Joined
22 Aug 2014
Messages
20
Reaction score
0
Location
Wiltshire
Country
United Kingdom
A wire from cylinder stat Sat terminal must also be connected to the grey wire/HW Sat, i.e. three wires connected together.

I'm assuming that's already in place at the wiring centre. As I'm connecting the HeatLink into the wiring at the programmer end, then it's not relevant. Whereas Stem's point about the 'HW Off' being connected to the 'Hot Water Satisfied' is valid.
 
Joined
22 Aug 2014
Messages
20
Reaction score
0
Location
Wiltshire
Country
United Kingdom
Thanks for all your help guys.

Finally tackled it today (wanted to wait until the other half was away for a few days in case it didn't go to plan).

All done and dusted in less than an hour. Everything connected and working like a dream.

Just wish I could've run a couple of wires from the Heat link to the thermostat, but got 2 door frames and walls in the way. Or replaced the existing thermostat and changed the wires, but wasn't possible. So at the moment the thermostat in on a table in the lounge. (I don't fancy having conduit on the wall).
 