Worcestor 28i

  • Thread starter Soggy_weetabix
  • Start date
S

Soggy_weetabix

I repair Worcestors a lot but I having a problem with (I think) the customer as opposed to the boiler.

Replaced PRV July 06 (filling loop letting by). 6 Months later customer informs me PRV has gone again.

Replaced under guarantee.

Filling loop disconnected, ex/vessel still holding approx 1bar charge and working and 2 months later same fault.

Customer states pressure has never risen above 2 bar when system is at max temp.

Replace again, and today (a month later) ...same fault.

Am I overlooking something stoopid here?

Mains not entering via plate by the way - checked it.

I really think its over pressurisation by customer but he catagorically (sic) he has never done that.

Any ideas?

David
 
Sponsored Links

Rob

Joined
14 Aug 2006
Messages
5,571
Reaction score
712
Location
London
Country
United Kingdom
Unless the pipe to the vessel is blocked but as you know the pressure would have to get to 3 bar still.

Unless of course its a faulty guage :eek:

p.s 1000!
 
Joined
23 Feb 2007
Messages
21,178
Reaction score
1,936
Location
Norfolk
Country
United Kingdom
As you all know I don't usually touch Worcesters other than basic servicing, but I have had 2 this week where the pressure gauge has a mind of its own :eek:
 
Joined
2 Mar 2007
Messages
3,441
Reaction score
69
Location
Lancashire
Country
United Kingdom
Soggy_weetabix said:
I repair Worcestors a lot but I having a problem with (I think) the customer as opposed to the boiler.

Replaced PRV July 06 (filling loop letting by). 6 Months later customer informs me PRV has gone again.

Replaced under guarantee.

Filling loop disconnected, ex/vessel still holding approx 1bar charge and working and 2 months later same fault.

Customer states pressure has never risen above 2 bar when system is at max temp.

Replace again, and today (a month later) ...same fault.

Am I overlooking something stoopid here?

Mains not entering via plate by the way - checked it.

I really think its over pressurisation by customer but he catagorically (sic) he has never done that.

Any ideas?

David


As Rob and Dave have already pointed out David.
Had this several times on my worcester's.

Replace the guage ;)
 
Sponsored Links
Joined
25 Aug 2003
Messages
10,668
Reaction score
64
Location
Surrey
Country
United Kingdom
rob884 said:
Unless the pipe to the vessel is blocked but as you know the pressure would have to get to 3 bar still.

Unless of course its a faulty guage :eek:

p.s 1000!

YAY well done you are getting to as sad as me, dave agile and the rest

YOU WILL BE OURS HA HA HA HA HA

also I have cleared many of those ridiculous ex vess tubes on these so I concur
 
Joined
24 Jul 2003
Messages
24,298
Reaction score
1,416
Location
London
Country
United Kingdom
The cavity behind where the guage connects blocks, too. 4mm screwdriver drills it out!
 