Cust said "It worked fine since it was installed 4 years ago. Went cold yesterday" (Tuesday this week)
Ricicle: no...bog standard 30A fusewire.
Shows you how much you can overload a 3036 without it popping.
Overloaded by 45%+....
If you want instantaneous tripping on a 3036, you need around 2x the rated....
Any less and it will hold. The greater the overload the shorter the time it will remain intact, though. But I imagine with a shower only being on for 10mins, it was quite happy....