Surely this has to be the most common cause of failure of wylex fuse boxes?
 
Crispy!

What did the owner say? "It worked OK for ages, thought it was fine!"
 
Sponsored Links
That's a really ancient fusebox - it's even got a wooden backing - I'm surprised it did not catch fire with such a load on it!
 
Crafty - Yes! Crispy!

Cust said "It worked fine since it was installed 4 years ago. Went cold yesterday" (Tuesday this week)

Ricicle: no...bog standard 30A fusewire.

Shows you how much you can overload a 3036 without it popping.

Overloaded by 45%+....

If you want instantaneous tripping on a 3036, you need around 2x the rated....

Any less and it will hold. The greater the overload the shorter the time it will remain intact, though. But I imagine with a shower only being on for 10mins, it was quite happy....
 