There you go straight out of the honeywell book.
electrical check for installed Sundial Y Plans to
help in commissioning and to pin-point the source
of any electrical problems.
Remember the Golden Rule when you have a
problem. First of all check your wiring. Only start
suspecting faulty components after you are satisfied
all wiring is correct.
The following notes will help to identify faulty
components.
Cylinder Stat
First of all, make sure you have wired to the correct
terminals.
Terminal C (common) is the Left Hand terminal.
Terminal 1 is the Middle terminal.
Terminal 2 is the Right Hand terminal.
Suspect the cylinder thermostat is faulty only if
Terminal 1 does not become live when calling for
Hot Water, or Terminal 2 does not become live
when satisfied. (Make sure that Terminal C is live in
both cases). While checking, disconnect Terminals 1
and 2 to prevent false readings due to backfeed.
Room Stat
1) Remove wire from Terminal 3.
2) Live to Terminal 1.
3) Turn stat to call, if no live on 3 then faulty.
Suspect the room stat is faulty only if Terminal 3 is
not live when calling for heat. (Make sure Terminal 1
is live). While checking, disconnect wiring from
Terminal 3 to prevent false readings due to
backfeed.
Mid-Position Valve
Suspect the V4073A valve is faulty only if the valve
does not operate as specified in the following
checks (these should be done in order 1, 2, 3, 4, 5
and 6).
Valve open for Heating only
1. Switch off mains supply. Disconnect Grey
and White wires from appropriate junction box
terminals. Reconnect both Grey and White
wires to permanent live terminal in junction box.
2. Switch on mains supply. Valve motor should
now move to fully open heating Port A. The
motor should stop automatically when Port A is
open, and stay in this position as long as power
is applied to White and Grey wires. When Port
A is fully open, the Orange wire becomes live,
to start pump and boiler.
Double check by feeling that Port A outlet is getting
progressively warmer.
Valve open for D.H.W. only
3. Switch off mains supply. The valve should now
automatically return to open D.H.W. Port B and
close Heating Port A.
4. Isolate Grey and White wires and make safe.
Remove cylinder stat wire from Terminal 6 in
junction box and connect to permanent live.
Switch on fused spur, cylinder thermostat
must be set to call for heat, pump and boiler
should start.
Valve open for both D.H.W. and Heating
5. Switch off mains supply. Replace cylinder stat
wire to Terminal 6. Isolate and make safe Grey
wire and connect White wire to permanent live.
Switch on mains supply, motor should now
move to mid-position and stop automatically.
Cylinder thermostat must be set to call for heat.
Both ports A & B are now open for Hot Water
and Heating. Boiler and pump should start.
Double check by feeling that pipe outlets from ports
A & B become progressively warmer.
6. Switch off mains supply, reconnect White and
Grey wires to junction box terminals.
If this check completes satisfactorily, the problem is
not the valve, but elsewhere in the circuit.
Programmer
Suspect the programmer only:
(a) After you have made sure that any links
required are in place,
(b) After you have made sure that the Programmer
has power – to the correct terminal,
(c) After you have made sure that the Programmer
timing is set up correctly (see individual
Programmer User Guide as appropriate),
(d) If live does not appear at Heating ON Terminal
when Heating only is selected on continuous or
timed,
(e) If live does not appear at Hot Water ON
Terminal when Hot Water only is selected on
continuous or timed,
(f) If live does not appear on Hot Water OFF
terminal with Hot Water OFF on programmer.