BAS has separated this discussion into two main areas.
The first he calls '17th Edition CUs' and the second 'Updating existing installations'
I just want to look at the first of these for the moment.
Why is it called '17th Edition CUs' when all of the discussion seems to hinge around section 314 of BS 7671, which is concerned with division of the installation. Note that it just says installation - meaning any type and size - not just domestic. I am not just being pedantic here - it is an important point.
The discussion also seems to focus on the provision of RCD protection within these 'CUs' - people really must stop calling them Consumer Units - the French think we eat them if we call them that - the term used by the UK in Annex ZA of BS 60439-3 in 1994 was Customer Distribution Board (CDB)
![Big Grin :D :D](data:image/gif;base64,R0lGODlhAQABAIAAAAAAAP///yH5BAEAAAAALAAAAAABAAEAAAIBRAA7)
It would appear then that we are only considering the application of 314 to a limited sub-set of electrical installations when, in fact, it applies to all electrical installations.
No doubt someone will correct me if I am wrong
- but the argument appears to be that a single protective device - an RCD in this limited appraisal - must not protect more than one circuit. Further to this, some appear to be suggesting that this is a 17th Edition thing.
Well let's take the last point first - the 'minimise inconvenience' term first came in with the 15th Edition - it was taken out in the Brown copy and it stayed out of the 16th Edition until the Green copy, when it suddenly came back.
Note that the Irish had the term in their 1991 Rules - so it is probably IEC or CENELEC drafting.
BTW the Irish had the equivalent of 314.1 (iii) "take account of danger that may arise from the failure of a single circuit such as a lighting circuit" in 1991 - we are just a bit slow
Now for those that decide that this, admittedly poorly drafted, regulation should be taken to mean that we cannot use a split bar CDB, and that we must use RCBOs, or should I say those horrible, usually single pole, electronically operated (so they need volts to work!), excuses for circuit protect - not that I am biased mind
- then how do you solve this -
A distribution board supplied by a distribution circuit (sub-main in old money) is protected at the main panel by a single overcurrent device, or maybe, in a large T.T installation, a single S Type or fully adjustable RCD . If it operates all of the circuits on the distribution board lose power.
Just think on this a minute - imagine yourself in a very large installation - if you cannot use a single device to protect your distribution circuit you cannot use a distributed system. That OK just wire all of the final circuits back to the main panel - job done (we will forget about the possibility of the main fuse blowing
Now what size cable to use - what is the voltage drop on a mile long final circuit
I think we have a problem here and any solution must work for ALL electrical installations.