Landlords test certificate.
Is a spur subject to the same limitations?
Spur or not is irrelevant. What's it supplying?
In this case is it a BS 1363 accessory, or a CU?
If the latter and not the former, please show how the 2.5mm² cable on a 32A breaker complies.
Are you of the belief that BS1363 FCUs are the only additional fusing method allowed on a ring and/or spur?
Are you of the belief that 433.1.204 allows anything else?
Where is this 2.5mm² cable protected by a 32A OPD?
House to shed 4.0mm² 32A MCB
Shed radial 2.5mm² 20A MCB
Sounds fine to me (in terms of CCC and OPDs)
Oh - and you think that the ring final on the 32A MCB is wired in something larger than 2.5mm²?
Here:
The swa is terminated in a box on the outside wall which is fed from an internal socket on a 32A ring circuit.
You may be right, but you're only guessing/assuming, possibly incorrectly. We know that the SWA is 4mm², so it would be far from beyond possibility that the cable connecting the SWA to the ring is also 4mm².
Here:
Well, it would be stupid to not use the SWA to connect to the ring. Terminate into the box, no connections, take the SWA inner sheath straight into the socket, job done. But you're right, it may not be 4.0mm²
The ring itself is obviously allowed to be wired in 2.5mm² on a 32A MCB. The question is about the spur cable and, as I've just written, you can only guess about the CSA of the cable between the ring and the (4mm²) SWA. Guessing is not good.
Agreed, but you are misrepresenting me - my point was that it MAY be 4mm² all the way to the ring. It is BAS, not me, who appears to be guessing/assuming that it isn't!
Of course it is relevant.
Let's try again.
Does a circuit supplying indeterminate loads which are not prevented from reaching 32A, on a 32A OPD, but wired using a cable with a CCC of < 32A comply with 433.1.1?
I'm guessing/assuming (and I feel I am on solid ground there), that the ring is wired using 2.5mm², not 4mm².
What the spur is wired in is of no relevance whatsoever.
Only, as you know, if it's a ring final. As for the spur, we know that most of it probably has a CCC of 32A, and your just guessing about the last few inches/feet.
Oh, I see. In that case, my mistake
.. and you're almost certainly correct.
I'm lost - I thought it was the spur that concerned you.
Since the ring final itself, wired in 2.5mm² cable and protected by a 32A MCB would (given a few caveats) be allowed to supply, say, 50 x 13A sockets or FCUs, I don't really see what point you are trying to make.
... but it is 'late on a Friday night' !