In a recent thread …
As you (and I) often say, a common problem which many people seem to have in relation to some of the regulations relating to bonding (be it ‘main’ or ‘supplementary’ bonding) is that any and every regulation which talks about details of bonding only applies if there actually are some extraneous-c-ps to bond.
Assuming you still agree with that, I assume that you will agree that, then, as you know, in relation to bathrooms etc. 701.415.2 says …
In order to decide whether any conductive parts entering a bathroom are ‘extraneous-c-ps’ the most obvious thing to do is to look to BS7671’s definition, which, as you know, is …
As I see it, the only potential that one could credibly imagine, say, an internal pipe introducing into a room would be the potential of the MET - do you believe that ‘counts’ and qualifies it as being an ‘extraneous-c-p’ as far as the room is concerned? I suppose it must - otherwise it’s unlikely that anything would ever count as extraneous to the room (but not extraneous to the property)!
However, if I understand correctly, you don’t really use the BS7671 definition to decide whether something is an extraneous-c-p (and may therefore need bonding) but, rather you use the criteria of 415.2.2 as a “test” of whether something is ‘extraneous’ (and may hence need bonding).
If that is correct, then, having now reflected (maybe for the first time!) on this … the criteria of 415.2.2 provide a test of whether supplementary bonding, if present, is adequate (although it’s hard to see that any credible SB bonding conductor could fail to satisfy the criteria!), but I’m struggling to see how it can be of any value in determining whether (currently absent) SB is required (i.e. whether something qualifies as an extraneous-c-p).
Consider an L conductor within something in a bathroom coming into contact with an exposed-c-p of the item. The potential of that exposed-c-p will (prior to a protective device operating) rise to a proportion of the supply voltage (above MET potential), the magnitude of that pd depending on the respective CSA’s of the L and CPC of the supply cable - by my reckoning, with a 230V supply, roughly 142V for 2.5/2.5mm² cable, 139V for a 1.5/1.0mm² cable and 115V for a 1.0/1.0mm² cable - certainly all well above 50V.
If an extraneous-c-p is (as commonly will be the case) in electrical continuity with something bonded to the MET (or, at least, earthed to the MET), then there will be such a pd (142V, 139V or 115V - all well above 50V) between the faulty exposed-c-p and the extraneous-c-p - despite the fact that, when measured, it is very likely that the resistance between exposed- and extraneous-c-ps (or between extraneous-c-p and MET) would be well below the ‘pass’ criteria of 415.2.2. Hence, unless I’m missing something, such a ‘test’ is meaningless in the absence of SB, isn’t it?
In other words, I can’t see why (in the absence of SB) a low resistance between a conductive part which enters the room and an exposed-c-p (or the MET) can, in itself, provide any reassurance that SB is ‘not required’ (or that the part should not be considered to be an extraneous-c-p).
I am therefore more than a bit confused by this one of the criteria (in 701.415.2) for omission of SB in bathrooms being permissible …
I was going to ask whether I am I perhaps misunderstanding the way in which you use the criteria of 415.2.2. as a ‘test’, but it seems that I would have to ask the same of 701.415.2!
As above, I think that I must be missing a lot here, or just being dim!
It is whether it is an extraneous-c-p (or exposed-c-p) to the more stringent equipotential zone of the bathroom which has to be limited by supplementary bonding to 50V in the event of a fault.
As I wrote briefly in that thread, it was only when I found myself writing in that thread that I realised that I need to try to get my head around some confusions and uncertainties about things which I had always ‘accepted’ without question - but I suspect I am just being dim or, at least, not thinking clearly enough! I’ve tried to think about this and express myself in some haste, so this may be a bit confused/confusing (as well as very lengthy)I might be missing something as well as I'm not sure why you are asking this after all this time. … Have you discovered something which has made unnecessary what we have been doing for ever?
Per the above, that regulation presumably can only apply if there are any extraneous-c-ps (‘extraneous’ to the bathroom), since what it is ‘requiring’ would be impossible in their absence.701.415.2 of BS7671:2018 said:Local supplementary protective equipotential bonding according to Regulation 415.2 shall be established connecting together the terminals of the protective conductor of each circuit supplying Class I and Class II equipment to the accessible extraneous-conductive-parts, within a room containing a bath or shower, including the following: ….
BS7671:2018 said:Extraneous-conductive-part. A conductive part liable to introduce a potential, generally Earth potential, and not forming part of the electrical installation.
… since, as above, I can’t see why (e.g. in the fault scenario I described) the situation would be any safer (in the absence of SB) even if the resistance form extraneous-c-p to MET were low enough to satisfy the 415.2.2 criteria (or, come to that if it were near zero!). In fact, if anything (albeit totally trivial), in the situation I described the ‘risk’ would tend to increase as that resistance reduced, because there would be less limitation of the current that could flow through a person, and the risk would decrease if the resistance were much higher than the 'maximum' required to satisfy 415.2.2, wouldn't it?! I’m confused!(vi) All extraneous-conductive-parts of the location are effectively connected to the protective equipotential bonding according to Regulation 411.3.1.2.
NOTE: The effectiveness of the connection of extraneous-conductive-parts in the location to the main earthing terminal may be assessed, where necessary, by the application of Regulation 415.2.2.