Recent content by Electrifying

  1. E

    Help Please - a bit of a puzzler!

    Hi John, I think you've started me thinking in the right direction now - I need to find the break in CPC continuity and I need to find what else is connected to this circuit apart from standard light pendants - is that what you're saying? Because, obviously, if it was just open circuit...
  2. E

    Help Please - a bit of a puzzler!

    Fitting a new light fitting, so using Zs to confirm CPC continuity. Haven't tested dead yet, but, like I said, I will do now. CU is spot on, no problems.
  3. E

    Help Please - a bit of a puzzler!

    RCD trips on difference of current between L & N, so would still trip without CPC continuity.
  4. E

    Help Please - a bit of a puzzler!

    That's to be my first port of call on Sunday, along with an inspection of each other lighting point on the circuit. Open circuit CPC wouldn't explain the N - E reading of 81v with the light switch off though - in fact it wouldn't explain why the alarm sounded on my meter when connecting the...
  5. E

    Help Please - a bit of a puzzler!

    Hi all, Could do with some help. At a house yesterday and came across a problem on the upstairs lighting circuit whilst testing. It's a three bedroom, traditional semi. TN-C-S MK 12-way, twin RCD board. With all other MCBs OFF, except for the lighting circuit, I attempted to...
  6. E

    Shower Cable in wall

    John, this statement is 10 x worse than the one about the '0.05' ........you're slipping. And 'Scoby_Beasley', you really need to make sure of your facts before posting advice. :)
  7. E

    Extractor Fan Isolator Switch????

    Yes, annoying, isn't it? You go over the top with the cooker circuit in your new kitchen, just in case - you run a 10mm cable on a 50 Amp MCB. You pop out with the missus to choose your nice new cooker and when it arrives the instructions tell you you should only connect to a 40 Amp, 6mm...
  8. E

    Extractor Fan Isolator Switch????

    I have only ever fitted one of these ceiling fan/lights, although I have come across a few, (both my mother and mother in law have them), but I have yet to come across one with it's own, seperate isolator. They utilise the existing lighting circuit via the existing light switch and you run a...
  9. E

    Extractor Fan Isolator Switch????

    The irony is in the fact that they are only isolating the 'Line' conductor by pulling the fuse - not the 'neutral'.......was I not clear?? :).......yet you need 3-pole isolation to work on a fan.
  10. E

    Extractor Fan Isolator Switch????

    I wasn't implying that either type of fan did/didn't require a seperate isolator - I was commenting on the reasons that Bernard gave for this seperate isolator. I was also commenting on what you termed 'true isolation'.........ironically, a spark can get the DNO in to pull the main fuse so...
  11. E

    Extractor Fan Isolator Switch????

    Would you concede that anything that could go wrong with the extractor fan in the bathroom could equally go wrong with a ceiling fan/light that you may have mounted in your living room?
  12. E

    Extractor Fan Isolator Switch????

    I was always under the impression that the reason for a seperate fan isolator was so that if the fan needed to be worked on, it could be done without having to isolate the lighting - which would obviously be an issue if the bathroom didn't have a window. The 'Electricians Guide to the...
  13. E

    ZS on a new installation

    Again, everybody goes around the houses to explain something that really is quite simple. Measuring R1 +R2 is one method of proving continuity of the circuit protective conductor within a circuit, before energising the installation. Measurement of R2, (also acceptable), is another method...
  14. E

    testing lighting circuits

    You're still going to have to undo the light fitting to access the CPC - so not going to help you, really. (unless it's a class 1 light fitting, of course)>
  15. E

    Gas pipe earth???

    The gas pipe doesn't need 'earthing' - it may require 'bonding' if it is deemed to be 'extraneous' where it enters the property.