    calculating maximum demand for an installation

    Well the only thing that you are doing 'wrong' is not applying diversity. I am going out for dinner in a short while and cannot spare the time tonight, I will try to reply Saturday with calcs with diversity applied, unless some other kind gent does so in the meantime. Suffice to say that...
  2. S

    No certificates for electrical work.

    "And there is more chance of hell freezing over than you getting prosecuted for non-compliance with the Building Regulations." Maybe but so what? Same can be said for speeding, shop lifting, stealing in general and even murder these days as the police are far too busy filing in forms that...
  3. S

    calculating maximum demand for an installation

    That must be some Hell of a clamp meter, I have not come across one that is able to calculate diversity as well :o
  4. S

    oven trips RCD

    JohnD it will if as I said the CCU is 2P as both P and N will be isolated from the oven. :wink:
  5. S

    Upgrading cooker - instructions quirey

    You seen the cost of copper and t/e over the past year!!
  6. S

    No certificates for electrical work.

    I agree Gary the 'system' is far from perfect. But the risks of non-disclosure are pretty significant as the OP implies above. Other than obvious signs such as changes in cable colour, different make accessories, date of manufactured accessories, visible disturbance to the building the worst...
  7. S

    oven trips RCD

    Simple test - the oven should be connected via a CCU (a 2P device). Isolate the cooker/oven using this CCU. Does the RCD trip? If yes your sparky should ,have red face. Turn on the CCU. Does the RCD trip? If yes the cooker manufacturer should have a red face.
  8. S

    No certificates for electrical work.

    Sarcasm is the lowest from of wit and he highest form of vulgarity. Facts remain - it IS the home owner that is prosecuted for work done that does not meet the building regulations. The onus lies with home owners to ensure that trades people follow the rules.
  9. S

    Upgrading cooker - instructions quirey

    As stated it depends on the cable run length from the CU to the CCU and outlet plate. Use this to determine the type of cable and its csa - http://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html
  10. S

    Clicking noise at CU after replacing dimmer switch

    "With regards to the load - that was the only light I was attempting to turn on so it can't be overloading." Sorry to disagree but it can be close to or exceeding the load with a single FAULTY light installation. If its getting hot then clearly something really amiss. I suggest you get a...
  11. S

    No certificates for electrical work.

    They have ways and means I promise you that they do. Do you know what a conveyance "search" is and what it involves?
  12. S

    Buzz free formula for 12v downlight circuits.......

    "is there anything else I can use to get around this? " Yes fit a good old florry. Most modern dimmers no longer need the 2x rule. It is cheap transformers that 'buzz' to be precise it is the laminations that 'buzz'. Magic formulae? No such thing as magic only common sense (and money)
  13. S

    calculating maximum demand for an installation

    Depends what form you are filling in. One for the sub-main or for the WHOLE installation.
  14. S

    Clicking noise at CU after replacing dimmer switch

    'Clicking' sounds at CU's can only be one of two things - (a) the load is marginal for the MCB rating as in its a 6A MCB and the actual load is close to or over 6A. That is the total load is marginal. Check this by switching on as many lights on the same MCB as possible until its tarts...
  15. S

    C27 programer

    The wiring that you describe is completely wrong. It shoud be S-Plan. There should be 2 x 2 port valves or one 3-port valve, If it has a spring return then it is a 2-port. Something odd there for starters. It is also most odd that you have no stats at all! Was the system installed by an...