Recent content by tcm

  1. T

    Alpha 240P boiler - How to grease fan motor?

    Many thanks for your reply. I have done the following: - followed your advice. - cleaned the fan impellers and body. - inserted a screw onto the flue duct near the pressure sensing tubes. i.e. hole in the flue duct from day 1. - lifted the flue hood so that it does not touch the primary...
  2. T

    Alpha 240P boiler - How to grease fan motor?

    My boiler is about 10 to 12 years old. Due to louder noise, I have removed the fan assembly from my boiler and cleaned the impellers and body. Does anyone know if I can grease the motor bearings? Any other advice how to grease it would be appreciated.
  3. T

    Alpha 240P combi boiler - Pilot light problems

    In the second problem, when the pilot light went out and after a few seconds, I heard a click sound and saw the gas valve control pushed out automatically. I think the gas valve shutdown due to no pilot flame sensed.
  4. T

    Alpha 240P combi boiler - Pilot light problems

    I have 2 problems. The first one is when I press down the gas valve control, the fan is at full speed, but after 10s, the pilot light does not come on. However, if I remove the combustion chamber front cover (i.e. the burners can be seen), and repeat the above procedure, the pilot light comes...
  5. T

    Help! No DHW on Alpha 240P boiler

    BTW, you need both DHW and primary flow microswitches to be enabled in order to enable other functions, so that the burner can be fired up for DHW. I hope this helps other users in the future.
  6. T

    Help! No DHW on Alpha 240P boiler

    At last, I found the problem. It was due to the primary flow valve not being able to maintain constant pressure on the pin and as a result the primary flow microswitch was not activated constantly. To be precise, initially the pin pushes against the microswitch for about a second and the pin...
  7. T

    Help! No DHW on Alpha 240P boiler

    I have tried using a new DHW temp sensor but still burner would not turn on. - Checked the modulating coil at about 6.5V when demanded and 1.4V when not demanded which I think is OK. - Checked pcb M3 connector, terminals 17 and 19 for fan at 240V at slow speed but will not go to 440V when...
  8. T

    Help! No DHW on Alpha 240P boiler

    Thanks to replies from ChrisR and Paul. When I turn the hot tap on, pin from diverter valve comes out and pushes against the microswitch. I have checked the pump and it runs. However, when I checked PCB M2 terminals 5 and 6, there was no 240V supply to the gas valve! According to the manual...
  9. T

    Help! No DHW on Alpha 240P boiler

    Thanks to the quick reply from Paul. Ok I'll follow section 8.35 of the manual when I receive the PRV next week. Before I drained down the boiler, the PRV allowed water to go out at 2.5 bar. Am I correct to say that after I drained down the boiler, the PRV got damaged, because it is now...
  10. T

    Help! No DHW on Alpha 240P boiler

    I’m a beginner on boilers. Before I drained down the boiler, I had DHW. I had the problem of over-pressure on the central heating reaching 2.5 bar after about 8 mins of switching on, which caused water to flow out of the external flow pipe. Therefore, I drained down the boiler and...