Hi all,
After some advice.
I'm xporting a PME supply to a timber shed/workshop with no extraneous-conductive parts. The supply will come from an aditional CU in the house with a 40amp MCB and the outbuildings will have the following circuits fed from a CU in the shed/workshop:
In my situation, will the armour of the 2 Core - 10mm2 PVC XLPE SWA be sufficent CPC to export the TN-C-S earth to the outbuildings or can I only earth the armour of the cable as far as the shed/workshop and then have to TT the outbuildings?
Thanks!