Bathroom circuit-breaker?

Joined
24 Jan 2012
Messages
11
Reaction score
0
Location
London
Country
United Kingdom
Sponsored Links
You already have a single RCD split ('16th edition') board, chances are your upstairs ring is already RCD protected and if your fancy bath and floor heating are off this then unlikely any extra RCD protection will be required

The electrician you are using will be aware of the requirements though...
 
salimfadhley,
Where are you getting the power from to feed these two items of equipment.
If it's a new circuit, back to the board you will require RCBOs as you have no spares coved by the RCD.
If you are taking the feed from a circuit that is not covered by the RCD again this will need to be upgraded to one that is, easiest method is using RCBO at board.
I assume the two items will both have a separate means of isolation and you submitted notification to the council for work in special locations?
 
I've had to halt building - when I inspected what the builders had done they appeared to have taken power from a wall-socket ring-main, which I do not think is acceptable.

I've told the builders that we need to fit additional isolation switches for each new service, plus a new RCBO which will serve both.

Is it acceptable to run both things from a single circuit-breaker?
 
Sponsored Links
What is the total output of your UFH and what output is the spa bath?
This combination will dictate the rating of the RCBO, it will need to be type tested for the MK board, so you require a MK RCBO.
Taking the feed from the RFC may well be okay.
 