Hi everyone
Pretty much the title really
We moved into this house in October, it has a Baxi neta tec 28 GA fitted with a hive thermostat for central heating control only wired to low voltage controls
Has been working fantastic but since we had our electric smart meter installed, the boiler likes to fire up all by itself.
It's 02.30 at the moment and the house is like a sauna. Looking at the hive logs, the heating must have come on whilst we were out yesterday as the home temp rose to 23c from about midday, but the hive wasn't 'calling' for central heating, we only have it set to 'manual' mode.
Can anyone advise what the likely issue could be?
We had an engineer out a few weeks ago who said it could be a faulty hive receiver calling for heating, this was all replaced.
He did note that the diverter valve was noisy? Could this cause our issue?
What I have noticed is, if when the heating is on (but hive is off) if I manually turn off the heating, power down the boiler from the power button on the controls, wait a minute or so, power it back up and return the boiler to HW + CH mode, it works fine for the next 12-24 hours.
Any ideas?
Pretty much the title really
We moved into this house in October, it has a Baxi neta tec 28 GA fitted with a hive thermostat for central heating control only wired to low voltage controls
Has been working fantastic but since we had our electric smart meter installed, the boiler likes to fire up all by itself.
It's 02.30 at the moment and the house is like a sauna. Looking at the hive logs, the heating must have come on whilst we were out yesterday as the home temp rose to 23c from about midday, but the hive wasn't 'calling' for central heating, we only have it set to 'manual' mode.
Can anyone advise what the likely issue could be?
We had an engineer out a few weeks ago who said it could be a faulty hive receiver calling for heating, this was all replaced.
He did note that the diverter valve was noisy? Could this cause our issue?
What I have noticed is, if when the heating is on (but hive is off) if I manually turn off the heating, power down the boiler from the power button on the controls, wait a minute or so, power it back up and return the boiler to HW + CH mode, it works fine for the next 12-24 hours.
Any ideas?