IEC60332-3 cable has a copper foil around the conductors, with a stranded drain wire running through it in contact with the foil.

With the drain wire earthed, could this be used for runs buried in a plastered wall less than 50mm from the surface without RCD protection?
 
Sponsored Links
Sponsored Links
You'll have to ignore Holmslaw. They make some sort of hooch made from coconut milk out there. By this time of the day he is out of his tree.

"wogga wogga" Holmey.

Back to your question.

Read 522.6.6

I do not see IEC60332-3 included in the earthed metallic coverings allowed.

IEC60332 refers to tests on electric and optical fibre cables under fire conditions and has nothing to do with physical protection from nails/screws etc...
 