cooker Electrics help

Joined
22 Apr 2008
Messages
2
Reaction score
0
Location
Manchester
Country
United Kingdom
I am fitting about to fit a new kitchen and currently have a standalone cooker which is currently supplied from CU by 32amp MCB and 6mm T&E to cooker socket which then feeds cooker @ 11.5kw via 6mm T&E

I want to change to

CU – 32amp MCB goes to cooker socket which goes to junction box which splits to 1) New Oven (5.7kw) via 6mm T&E
2) New Hob (4.3kw) via 6mm T&E

is this acceptable from regs point of view. Also seeing as I then only have to put Junction box at end of current cable and hook up to oven & hob. Is this change Part P

The following website

http://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html

says that based on the specification below
Twin & earth
Crawl space, & clipped to wall
Load 10W
Voltage 230
Length of cabling 10m

that 6mm is acceptable - see below

Required cable size = 6mm
Voltage drop 3.2 volts
Percentage drop 1.4%
Load = 43 amps
 