Does an external earthy clipped to the wall need protetion??

Joined
1 Dec 2007
Messages
82
Reaction score
1
Location
Derbyshire
Country
United Kingdom
Reposted to generate a new audience on this specific point.

If I run a main earth from the consumer unit to the incoming water supply, in 10mm cable clipped above external ground level, does it need to have any extra protection. Ref to any laws please this is within part P

Cheers.
 
Sponsored Links
Is the earthing conductor being run outside?
If this is so, it should be protected mechanically and against corrosion.
Also your earth label should be suitable for the environment.
Sorry edit "earthing conductor" to bonding.
Still needs to be protected against environmental conditions.
 
Sponsored Links
It needs to be properly insulated, that's for sure.

Or it will become an extraneous-conductive-part, and require bonding where it enters the house near to the CU....
 
I have editted my original reply;
Sorry edit "earthing conductor" to bonding.
The cable will still ideally need to be protected against environmental conditions.
 