I need to extend a ring cirucit in the middle, basically it comes out of the floor and need to make part of the cable longer.

I was going to use something like this:
http://www.screwfix.com/p/30a-3-terminal-junction-box-white/5866d

or

http://www.screwfix.com/p/chocbox/54936

My question is, these are rated to 30A, but the ring circuit im using (kitchen) has a 32A breaker. Are they ok to use, or do i need to find a beefier juntion box?

Im reading conflicting answers on this. Its odd as Junction boxes seem to be 30A or way over that, nothing in between.

Thanks.
Dan
 
Last edited:
Sponsored Links
Would be fine, on a 2.5mm ring the cable only could be rated 27A if clipped to the wall anyway.
 
My question is, these are rated to 30A,
The 30A ones are.

but the ring circuit im using (kitchen) has a 32A breaker. Are they ok to use, or do i need to find a beefier juntion box?
They're fine. Don't forget that there are two cables in a ring.

Be aware that those junction boxes must remain "accessible" for inspection, especially the chock-box ones - i.e. cannot be hidden away.

These can be
https://www.tlc-direct.co.uk/Products/ASJ803.html
 
Sponsored Links
Thanks both of you once again. That exactly what i needed to know and makes complete sense now :)
 