garage

Joined
27 Dec 2005
Messages
9
Reaction score
0
Location
Pembrokeshire
Country
United Kingdom
hi i wander if any one cane help? i'm running power to my garage from my house i'm using 4mm swa. the problem is it just makes it to the garage and i want to join on ordenary 4mm cable do i need a spiecal conection? plus do i need to have a earth rod connected to the garage unit thanks
 
Sponsored Links
Jimyboy..the link from your supply to the garage should be solid..that is unbroken from one protective device to another.

If you do not know the type of joint kit you need to join cables then you don't know how to use them correctly, and thus should not be contemplating this venture.

Are you sure that 4mm² SWA is sufficient for yopur needs regardiong the potential loading on the supply?

Do you know how to calculate the Volt drop on a given cable?

Do you have access to a Regs book or onsite Guide so that you can check the maximum current carrying capacity of a given cable and it's volt drop per ampere per meter?

If the answer to the above is Yes..do you know how to properly read and interpret the data sets in the tables?

Is this SWA two core or three core??

Are you intending to install and RCD at either end of the cable?

Do you know how to install the devices to ensure correct discrimination occurs in the event of a fault?


How much do you understand about this type of installation?

Answer those questions and perhaps you can get some advice...
 
jimyboy said:
hi i wander if any one cane help?
We'll do our best

i'm running power to my garage from my house i'm using 4mm swa.
Ok

the problem is it just makes it to the garage and i want to join on ordenary 4mm cable do i need a spiecal conection?
You mean T&E ? I wouldn't, I'd extend the SWA; adaptable box, BW SWA glands and yellow insulated crimps

plus do i need to have a earth rod connected to the garage unit
The 'unit' would be a CU? right? and I don't know, what are the earthing arrangements on the board that supplies this submain?


You're welcome
 
Sponsored Links

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back