heating on when not required

Joined
7 Oct 2012
Messages
2
Reaction score
0
Location
Sussex
Country
United Kingdom
I am working on a potterton prima f boiler with 2 x 2 port danfoss valves I am not sure which make of programmer the problem I have got is the boiler works fine on hot water when calling for demand but on the heating side there is no control the room stat is on 0 the programmer is is off and I have also removed the programmer from the wall but the boiler still fires up can you help
Thanks
oggy morris
 
Sponsored Links
CH valve end switch still closed. If you are qualified and"working on a Prima boiler" you should be able to work out what is wrong.
What other fault finding have you done on this system, and have you got a multimeter? Those heads are removable so you can check the valve spindle etc.
 
Hi pete i am newly qualifid. I think i have worked it out if the ch valve has
gone to an open circuit it would then power up the boiler is that correct Gary
 
Sponsored Links
No, that is not correct. You have an S Plan system, and one of the switches in one of the power heads is remaining closed and sending a feed to the boiler via the orange wire. Google S plan diagram and study it to get to grips with the way it works.
 