installing electric oven
17 Jan 2004
I've just bought a new Neff double oven - www.neff.co.uk/U1422.html. Very nice and shiny it is, too.
I've searched the forum on this topic, and come up with a few similar issues - but nothing that quite matches.
The oven isn't supplied with a connection cable :rolleyes: and the manual tells me I need a cable H05RR-F 3 G 1.5
I've looked at the wire coding system in this post:
//www.diynot.com/forums/viewtopic.php?t=11233&highlight=HO5, but I just want to confirm that this is specifying 1.5mm cable?
Oven is rated at 4.6KW. Old (single) oven was 2.1KW - can I use the cable from that oven?
Cooker circuit itself is fine - newish house.
What is this "cooker circuit" you speak of? What size cable supplies it? What is the rating of the circuit protective device? Is there an electric hob on the same circuit?
This oven is more than double the rating of the old one, the wiring may have only been designed for the old oven.
It's a 32A circuit - not sure of cable size, but house was built in 1992 (have the regs changed significantly since then?). Cooker is the only item on the circuit. Cooker switch doesn't have a socket. Cooker switch feeds a 13A FCU in the cupboard beneath the oven.
I've just checked the old oven cable and it's only 1mm - so I'll need to but some 1.5mm anyway.
So you have a 32A MCB feeding a cooker switch, which in turn feeds the 13A FCU? And there is no electric hob?
Right, for this oven, remove the FCU (the oven is now >13A) and replace with a cooker outlet plate. Use the same size cable as the rest of the circuit (6mm²?) to make the final connection to the oven.
That old oven should never have been connected in 1.0mm².
For correct protection of the oven you should change the protective device for a 20A MCB (4.6kw is spot on 20A at 230V), but it should be ok at 32A, as a 20A would be sometimes running at limit which isn't good for it.