Right,
Sorry bit of an idiot.
I checked the actuator and realised how easy it is to take on and off.
Checking the valve behind, there is some movement but how much is there meant to be?
If its closed position is 12 o'clock the only movement is to the left to about 9 o'clock. Should it move the other way? (to the right) or is this its normal movement.
Cheers guys
Russell,
If it is like a standard 3-way diverting valve, from memory, I think it turns through 90 Degrees stroke to stroke, at one extreme it is on hot water only, at the other extreme it is central heating onlly and at mid-posiiton (I believe this is what you are describing as 12 o' clock) it is feeding heat to hot water AND central heating.
Basically, if it doesn't turn through the same stroke as the actuator ( assuming it is the right actuator, 99% certain it must be or it wouldn't fit on easily) then it is stuck, probably from being scaled up or seized up due to old age, no inhibitor etc.
If so, just change it, not worth messing around trying to free it up.
In the meantime, I'll try and find a data sheet for your valve, will post back.
Hope this helps.
Rob