Hi All,
I have problems with low pressure/flow rate in my house (in North Cornwall).
I have a combi system with no space for a header tank, meaning running a bath (or two people using hot water simultaneously) has a very low pressure/flow.
I already had a plumber who said the problem stemmed from the water main into the house (he cleaned out the pressure reducing valve and turned it right down to negligible effect). He then recommended I call out the water board for them to perform some tests from the roadside.
When the water board came to visit, he connected a large tap to the water main outside my house on the street and did 2 tests.
1) He connected a pressure dial - about 1.95 bar pressure
2) He used a metal pot with holes in it to approximate the flow rate (about 38 litres per minute).
He said these were perfectly healthy, so pointed back towards the house.
Then he repeated the test with the outside tap adjacent the kitchen sink (close to the water main, but within the property).
1) Pressure dial was actually a bit higher (2.1 bar)
2) Flow was about 20 litres per minute,
He told me that I should remove the Pressure Reducer valve entirely, saying water pressure across the entire area was being reduced and there was no prospect of it ever being dangerously high.
My questions is: Is the Pressure Reducer required by law? and does anyone have any experience with pressure reducer valves having such a negative effect to pressure and flow?
I have problems with low pressure/flow rate in my house (in North Cornwall).
I have a combi system with no space for a header tank, meaning running a bath (or two people using hot water simultaneously) has a very low pressure/flow.
I already had a plumber who said the problem stemmed from the water main into the house (he cleaned out the pressure reducing valve and turned it right down to negligible effect). He then recommended I call out the water board for them to perform some tests from the roadside.
When the water board came to visit, he connected a large tap to the water main outside my house on the street and did 2 tests.
1) He connected a pressure dial - about 1.95 bar pressure
2) He used a metal pot with holes in it to approximate the flow rate (about 38 litres per minute).
He said these were perfectly healthy, so pointed back towards the house.
Then he repeated the test with the outside tap adjacent the kitchen sink (close to the water main, but within the property).
1) Pressure dial was actually a bit higher (2.1 bar)
2) Flow was about 20 litres per minute,
He told me that I should remove the Pressure Reducer valve entirely, saying water pressure across the entire area was being reduced and there was no prospect of it ever being dangerously high.
My questions is: Is the Pressure Reducer required by law? and does anyone have any experience with pressure reducer valves having such a negative effect to pressure and flow?