Solar inverter on dual RCD board

bsr

Joined
5 Aug 2008
Messages
961
Reaction score
111
Location
Gloucestershire
Country
United Kingdom
Hi

I have a modern (steel) dual RCD board. My solar inverter is on a dedicated circuit with a B20 MCB on one of the two RCD segments.

Am I right in thinking this is bad practice as it means the RCD tripping won't prevent current flow to the circuits fed by that RCD for the three second permitted shutdown time?

How important is it to resolve and what's the simplest way? I could move the solar circuit to before the first RCD but then it won't be on the busbar segments so I'll need some chunky tails to join to the first RCD. Do you use 25mm or is there something specific?

I have a third neutral bar in the CU.

Thanks
 
Last edited:
Sponsored Links
Hi

I have a modern (steel) dual RCD board. My solar inverter is on a dedicated circuit with a B20 MCB on one of the two RCD segments.

Am I right in thinking this is bad practice as it means the RCD tripping won't prevent current flow to the circuits fed by that RCD for the three second permitted shutdown time?

How important is it to resolve and what's the simplest way? I could move the solar circuit to before the first RCD but then it won't be on the busbar segments so I'll need some chunky tails to join to the first RCD. Do you use 25mm or is there something specific?

I have a third neutral bar in the CU.

Thanks
It's not just bad practice - it's prohibited.
 
Interesting, I have just posted about using an RCD and it has been pointed out they in the main are directional due to the electronics, so the solar inverter must feed the correct side of the RCD.
 
Sponsored Links
Interesting, I have just posted about using an RCD and it has been pointed out they in the main are directional due to the electronics, so the solar inverter must feed the correct side of the RCD.

not sure I agree with “correct side” statement
 
If you can find a reg then I can call back the company (y)

Any advice on moving the MCB to the non load side as above?
 
If you can find a reg then I can call back the company (y)

Any advice on moving the MCB to the non load side as above?

If the pv is on a shared RCD , that side of the board will be unable to comply with the necessary disconnection times
 