Supply to a garage with TT to house

Sponsored Links
Wouldn't apply on an all RCBO set-up though would it. (assuming no up-stream TD RCD)

You can't really get away from having an upstream RCD as the feed to the outbuilding will be in SWA or similar.

I was just drifting away from the topic with regard to Rob's general statement about single pole RCBOs being forbidden in TT systems :oops:
 
Yeah, I'll look that up, but I seem to remember it being the case, even for an all RCBO setup :confused:
 
Didn't think they were explicitly forbidden, but they won't clear N/E faults, so 100ms later the incomer will trip, and take out the whole installation, which could be construed as a contravention...
 
Sponsored Links
I know the regs say that in a system other than TN that circuits must be disconnected from all live conductors but one switch can fulfil this for a number of circuits ie a main switch.
 
Didn't think they were explicitly forbidden, but they won't clear N/E faults, so 100ms later the incomer will trip, and take out the whole installation, which could be construed as a contravention...

Only if there's a RCD upstream which needn't be the case in an all RCBO set-up.
 
True - I was thinking about the traditional 16th TT CU, but with RCBOs instead of a split with a 30mA RCD....
 
From a non regs POV if you had a fault causing a N-E short on a single RCD pole protected circuit on a TT system then you'd end up with a pretend TN-CS system which could be dangerous.
 