Some off the posters on here have hit the nail on the head and some are talking cr@p.
You have a blocked domestic heat exchanger (other name is water to water heat exchanger).
One question, have you ever had your CH system cleaned?
More likely NO........you need to clean your CH system to prevent fault coming back in a few months time first of all, second (if you have time) you need to take the heat exchanger off (really easy should take 5 mins) clean it out with a industrial strength drain cleaner I use shift-it works a treat. BUT ONLY PUT IT IN THE CH SIDE NOT THE DHW. leave in for a couple of days wash out and re-fit.
The other way is purchase a new heat exchanger (about £80) and swap out only take about 30 mins.
Don't throw away the old heat exchanger you can still clean it and put it aside as a spare.
You have a blocked domestic heat exchanger (other name is water to water heat exchanger).
One question, have you ever had your CH system cleaned?
More likely NO........you need to clean your CH system to prevent fault coming back in a few months time first of all, second (if you have time) you need to take the heat exchanger off (really easy should take 5 mins) clean it out with a industrial strength drain cleaner I use shift-it works a treat. BUT ONLY PUT IT IN THE CH SIDE NOT THE DHW. leave in for a couple of days wash out and re-fit.
The other way is purchase a new heat exchanger (about £80) and swap out only take about 30 mins.
Don't throw away the old heat exchanger you can still clean it and put it aside as a spare.