I don't think they have for extensions to dwellings.New Part L nosey!
Have the U-values changed in the latest revision? I thought not?
the U-values for the walls to extensions is unchanged at 0.28 W/m2K under the latest 2013 edition of Part L1/B.
The only time lower wall U-values are required for extensions, is if the extension has a higher than the permitted amount of openings, in which case a calculation must be carried out to offset the extra heat lost via the openings, by reducing the U-value of the other elements (floors, walls, roof)
The requirement for openings to extensions is to add the area of any existing openings which as a result of the extension are no longer exposed, to a figure representing 25% of the total floor area of the extension. provided the elemental U-values are then achieved in the floor walls and roof, the extension will comply with AD-L1/B.