Cause of electric shower failure


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
williaminsurrey

from United Kingdom

Joined: 08 May 2007
Posts: 15
Location: Surrey,
United Kingdom

PostPosted: Wed Apr 10, 2013 5:26 pm Reply with quote

Hi Experts,

My Mira sport max 10.8kw shower gave up the ghost last week. When I turned it on for the last time there was a loud ‘pop’ or ‘bang’ then shower went dead (panel lights went off). What worries me is that the RCD that supplies the shower (Wylex, 80A, 30mA) didn’t trip. I have since tested the RCD using the yellow button on the RCD itself (simple test, I know) and it seemed to work fine.

So my question is: What kind of catastrophic failure in the shower would not cause the RCD to trip?

A bit more information. There was some brief warning that something wasn’t right with the shower. About an hour before the final failure, water started flowing from the shower spontaneously without me turning it on (although there was power to the shower). The flow did eventually stop after a few minutes, although my pressing the ‘off’ button didn’t seem to have much effect. I later took off the front cover and couldn’t see any obvious signs of water ingress or electrical failure (see photo).

Thanks for any help.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
viewer

from United Kingdom

Joined: 02 Apr 2005
Posts: 772
Location: United Kingdom
Thanked: 52 times

PostPosted: Wed Apr 10, 2013 5:42 pm Reply with quote

Failure is on circuit board which has working parts which are not directly connected to the mains supply. A small transformer turns the 230V to whatever is needed on the board (maybe 5 - 24 V) No idea what went wrong, but a capacitor failing can make an amazing bang for such a small item. There would be no danger. If the failure had caused a short to neutral or earth then the MCB or RCD would have tripped.
Back to top
 Alert Moderators
Robin0577

from United Kingdom

Joined: 16 Aug 2011
Posts: 249
Location: London,
United Kingdom
Thanked: 44 times

PostPosted: Wed Apr 10, 2013 6:22 pm Reply with quote

I would agree with something on the printed circuit board having gone pop.

Usually there is evidence, i.e. scorch marks or debris and often an unpleasant smell, so I would assume it's something on the far side of the board we can't see in the picture or possibly even on a second board underneath?
Back to top
 Alert Moderators
JohnW2

from United Kingdom

Joined: 28 Jan 2011
Posts: 15643
Location: Buckinghamshire,
United Kingdom
Thanked: 881 times

PostPosted: Wed Apr 10, 2013 6:30 pm Reply with quote

williaminsurrey wrote:
My Mira sport max 10.8kw shower gave up the ghost last week. When I turned it on for the last time there was a loud ‘pop’ or ‘bang’ then shower went dead (panel lights went off). What worries me is that the RCD that supplies the shower (Wylex, 80A, 30mA) didn’t trip. I have since tested the RCD using the yellow button on the RCD itself (simple test, I know) and it seemed to work fine.
So my question is: What kind of catastrophic failure in the shower would not cause the RCD to trip?

I take it that the MCB protecting the shower circuit didn't trip, either? In addition to what viewer has said (very probable answers), there are plenty of catastrophic things that could happen which would trip an MCB but not an RCD - only a fault allowing current to flow from live to earth would cause an RCD trip. A fault from live to neutral would trip the MCB, but not RCD.

Kind Regards, John
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17227
Location: Leeds,
United Kingdom
Thanked: 894 times

PostPosted: Wed Apr 10, 2013 8:51 pm Reply with quote

Assuming there is an MCB of course icon_wink.gif
Back to top
 Alert Moderators
JohnW2

from United Kingdom

Joined: 28 Jan 2011
Posts: 15643
Location: Buckinghamshire,
United Kingdom
Thanked: 881 times

PostPosted: Wed Apr 10, 2013 9:00 pm Reply with quote

RF Lighting wrote:
Assuming there is an MCB of course icon_wink.gif

Indeed so. We've seen a good few examples of 'shower CUs' fed straight from pre-CU Henleys which contain pretty RCDs and nothing else!

Kind Regards, John
Back to top
 Alert Moderators
williaminsurrey

from United Kingdom

Joined: 08 May 2007
Posts: 15
Location: Surrey,
United Kingdom

PostPosted: Wed Apr 10, 2013 9:41 pm Reply with quote

Thanks for all of your replies - very helpful. Yes, the shower is fed by a Wylex 50A MCB, which didn't trip.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Shower Failure 15 780 Fri Dec 03, 2004 1:17 pm
Failure to notify, the costs & time limits etc? 2 660 Mon Oct 20, 2008 8:48 am
Ceiling Light Fitting - Sudden Failure 6 500 Sat Jul 05, 2008 4:55 pm
Lighting failure in kitchen - please help 4 280 Sat Nov 29, 2008 3:09 pm
Device to alert you to a power failure 4 400 Sun Jan 04, 2009 1:49 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.