andrewc1

Joined: 29 Aug 2011 Posts: 4 Location: London, United Kingdom
|
Posted: Mon Aug 29, 2011 6:40 pm |
|
|
Hello,
I hope this isn't a silly question, but if it is, please bear with me as I'm not an electrician and I've only started learning about these things recently.
Along with the other three residents, we're jointly responsible for the maintenance of the common areas of my block of flats. Electrically, there's not much in the common areas - some lights, one 13A socket and a door entry system.
In looking around the basement, it seems that the electricity supply for the common areas comes via the meter into the bottom of a metal box, which I gather is called a cutout. This box looks to be iron (as it looks rusted), has a metal up/down switch, has its cover missing, and has two ceramic 15A fuseholders - one for live and one for neutral. And directly above, three cables are connected - 3 live wires to live terminal, 3 neutral wires to neutral terminal. These cables are the lighting/entry circuits - there is no consumer unit.
From what I've gathered, I should phone UK Power Networks and they'll come out and replace this whole setup with something more 21st century. However I'm concerned that when they come, they might say that what is on our side of the cutout is unsafe, and as a consequence disconnect us from the mains.
So I guess I'm basically asking two questions:
- Is our side of this setup safe/within regulation?
- And secondly, if something is wrong, will the engineer cut us off? If this is probable, should we first contact an electrician to fix our side before involving the DNO?
Thanks for reading this, and all advice will be much appreciated. |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
flameport

Joined: 10 Mar 2007 Posts: 3560 Location: Bournemouth, United Kingdom Thanked: 531 times
|
Posted: Mon Aug 29, 2011 6:44 pm |
|
|
| andrewc1 wrote: | | the electricity supply for the common areas comes via the meter into the bottom of a metal box |
If this box is after the meter, then it is your responsibility to maintain or replace it.
Your supplier will only replace items before the meter.
Pictures of the equipment will help. |
|
| Back to top |
|
|
|
 |
westie101

Joined: 03 Jan 2011 Posts: 1517 Location: Cumberland, United Kingdom Thanked: 157 times
|
Posted: Mon Aug 29, 2011 6:44 pm |
|
|
Any thing before the meter is the responsibility of UK Power Networks. Anything after the meter is the customer's responsibility.
A photo would be useful |
|
| Back to top |
|
|
|
 |
Spark1964

Joined: 29 Aug 2011 Posts: 12 Location: Lancashire, United Kingdom
|
Posted: Mon Aug 29, 2011 7:25 pm |
|
|
- Is our side of this setup safe/within regulation?
Sounds like it isn't I'm afraid. If you have a switchfuse that has no cover and no circuit separation / protection then chances are it is pretty old and quite possibly dangerous.
Are you the joint owner of the property or a tenant, as if you are the latter, then no tenancy agreement should place the owness of electrical safety on you.
If you are the owner then you really should get this looked at by a pro - again pics would help.
2nd point on cut off bt the REC - Unlikely from what you have said but if the installation is seriously dangerous then this is a possibility.
The sensible thing to do is get it inspected asap, then decide who is responsible. |
|
| Back to top |
|
|
|
 |
securespark

Joined: 11 Jan 2004 Posts: 22532 Location: Cheshire, United Kingdom Thanked: 306 times
|
Posted: Mon Aug 29, 2011 11:44 pm |
|
|
|
|
| Back to top |
|
|
|
 |
ericmark

Joined: 27 Jan 2008 Posts: 5649 Location: Flintshire, United Kingdom Thanked: 456 times
|
Posted: Tue Aug 30, 2011 5:15 am |
|
|
My understanding is before one can make a dwelling uninhabitable one has to ensure there is alternative accommodation for the inhabitants. To remove the electric supply is considered as making the dwelling uninhabitable so is not done without very good reason. It is therefore unlikely that the DNO would remove the supply and if they did then it would be very dangerous so not a bad thing anyway.
However it seems unlikely the faults are on DNO side of the meter so I would get an electrician to look at it first.
Although one may get neutral links it is unlikely the neutral is fused. To fuse the neutral can be dangerous. |
|
| Back to top |
|
|
|
 |
OwainDIYer

Joined: 05 May 2010 Posts: 2050 Location: Stirlingshire, United Kingdom Thanked: 269 times
|
Posted: Tue Aug 30, 2011 8:58 am |
|
|
| ericmark wrote: |
Although one may get neutral links it is unlikely the neutral is fused. To fuse the neutral can be dangerous. |
Double-pole fusing was routine until about WW2. |
|
| Back to top |
|
|
|
|
|
 |
andrewc1

Joined: 29 Aug 2011 Posts: 4 Location: London, United Kingdom
|
Posted: Tue Aug 30, 2011 10:39 am |
|
|
Thanks to everyone for their replies. I'll put up a photo when I get home tonight.
In response to securespark, the box we have looks much older than the link. And in response to Spark1964, I am a leaseholder, and the leaseholders are collectively responsible for building maintenance, so ultimately it does become my problem. |
|
| Back to top |
|
|
|
 |
andrewc1

Joined: 29 Aug 2011 Posts: 4 Location: London, United Kingdom
|
Posted: Tue Aug 30, 2011 7:06 pm |
|
|
Photos of the bottom of the meter
and of the cutout
I hope they're clear enough, if not I can enlarge them and upload with better quality. |
|
| Back to top |
|
|
|
 |
westie101

Joined: 03 Jan 2011 Posts: 1517 Location: Cumberland, United Kingdom Thanked: 157 times
|
Posted: Tue Aug 30, 2011 7:15 pm |
|
|
That's not the cut-out. Sadly that is "your" property so sadly your problem.
As has been suggested you need to get an electrician in immediately
(if DNO staff saw that they would at the very least give you legal notice to get it sorted) |
|
| Back to top |
|
|
|
 |
RF Lighting

Joined: 31 Mar 2006 Posts: 16141 Location: Leeds, United Kingdom Thanked: 718 times
|
Posted: Tue Aug 30, 2011 7:19 pm |
|
|
It might be prudent to have the DNO pay a visit too. The trebling up on the meter input isn't too clever.
We could do with a wider photo showing everything in one shot if possible. |
|
| Back to top |
|
|
|
 |
dormermike

Joined: 01 Mar 2011 Posts: 433 Location: Cardiff, United Kingdom Thanked: 9 times
|
Posted: Tue Aug 30, 2011 9:50 pm |
|
|
Jesus that looks lethal |
|
| Back to top |
|
|
|
 |
ban-all-sheds

Joined: 27 Aug 2003 Posts: 41395 Location: London, United Kingdom Thanked: 1337 times
|
Posted: Tue Aug 30, 2011 11:04 pm |
|
|
It is.
Electrician needed as a matter of urgency. |
|
| Back to top |
|
|
|
 |
andrewc1

Joined: 29 Aug 2011 Posts: 4 Location: London, United Kingdom
|
Posted: Wed Aug 31, 2011 7:07 pm |
|
|
Thanks again to everyone for the replies. I guess it's pretty clear what needs to happen next.
I was thinking about pulling that metal lever down to shut off the electricity so that I could add in a light switch (!) into one of the circuits, but not any more. In fact I'm now afraid to touch any part of this setup. |
|
| Back to top |
|
|
|
|
|
 |
|
|