Alpha CB28 No hot water


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
lisa31

from United Kingdom

Joined: 13 Apr 2011
Posts: 15
Location: United Kingdom

PostPosted: Mon Oct 10, 2011 6:59 pm Reply with quote

Hi,
Have posted on here before and got great advice and help so am back again for more....CB28 had a new diaphram few months back and all was good then all of a sudden im not getting hot water, sometimes it works...and sometimes it point blank refuses and both the red and yellow neon lights flash alternatly, i can sometimes get it going again by reseting it.
I am thinking it may be the DHW switch thingy.....if it is...and me being a woman...would i be able to replace it myself or do i have to phone the uncle who fixes boilers but also drives me scatty ( think the chuckle brothers )

Any help would be appreciated...thank you icon_smile.gif
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Rob

from United Kingdom

Joined: 14 Aug 2006
Posts: 4228
Location: London,
United Kingdom
Thanked: 347 times

PostPosted: Mon Oct 10, 2011 7:09 pm Reply with quote

Red and yellow alternating would indicate faulty pressure switch.
Back to top
 Alert Moderators
jasongates

from United Kingdom

Joined: 06 Mar 2011
Posts: 14
Location: Sussex,
United Kingdom
Thanked: 1 time

PostPosted: Mon Oct 10, 2011 7:12 pm Reply with quote

Or that your system pressure is too low, what is your pressure gauge showing?
Back to top
 Alert Moderators
heatech2301

from United Kingdom

Joined: 06 Oct 2011
Posts: 2
Location: Suffolk,
United Kingdom

PostPosted: Mon Oct 10, 2011 7:13 pm Reply with quote

hi read your problem its the microswitch just requires the thin metal plate bending a little this should cure your problem and yes providing you isolate the power to the boiler it should cure if in doubt get a pro in hope this helps ....
Back to top
 Alert Moderators
nickso

from United Kingdom

Joined: 30 Oct 2006
Posts: 6378
Location: United Kingdom
Thanked: 236 times

PostPosted: Mon Oct 10, 2011 7:15 pm Reply with quote

heatech2301 wrote:
hi read your problem its the microswitch just requires the thin metal plate bending a little this should cure your problem and yes providing you isolate the power to the boiler it should cure if in doubt get a pro in hope this helps ....


er......no. icon_lol.gif
Back to top
 Alert Moderators
lisa31

from United Kingdom

Joined: 13 Apr 2011
Posts: 15
Location: United Kingdom

PostPosted: Mon Oct 10, 2011 7:39 pm Reply with quote

System pressure is fine, i think, 1.5 when cold ( in the green bit on the dial ) and rises to 2 when the heating is on ? all radiators have been bled and all get hot when the heating is on.

I dont mind having a go at things myself if i know im not going to blow up ha
Back to top
 Alert Moderators
compheat

from United Kingdom

Joined: 22 Nov 2005
Posts: 1938
Location: Lancashire,
United Kingdom
Thanked: 326 times

PostPosted: Mon Oct 10, 2011 8:29 pm Reply with quote

Rob wrote:
Red and yellow alternating would indicate faulty pressure switch.


A and B flashing (both red) alternately idictate a pressure problem.
I didn't realise that both the red and yellow lights flashed.

A=Red
B=Red both fault lights
C= burner lit
D= power on
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52905
Location: London,
United Kingdom
Thanked: 3331 times

PostPosted: Mon Oct 10, 2011 11:45 pm Reply with quote

I did not remember this boiler has a pressure sensor.

Lisa, regardless of the dial pressure, increase it a little as the indication seems to indicate the electronics thinks its too low.

Tony
Back to top
The following user says thank you to Agile for this useful post:
lisa31 (11 Oct 2011)
 Alert Moderators
DP

from United Kingdom

Joined: 10 Dec 2003
Posts: 6503
Location: Glasgow,
United Kingdom
Thanked: 747 times

PostPosted: Tue Oct 11, 2011 5:50 am Reply with quote

Quote:
hi read your problem its the microswitch just requires the thin metal plate bending a little this should cure your problem and yes providing you isolate the power to the boiler it should cure if in doubt get a pro in hope this helps ....


If indeed the plunger fails to operate the switch, then there would be a reason for that not happening. BENDING the lever is NO cure. Poster, will you take the responsibilty of dealing with the boiler if burner fires up and melts the combustion chamber because there is no water in the system but the lever has been BENT to initiate ignition sequence? I think not- act responsibly.
Back to top
 Alert Moderators
Rob

from United Kingdom

Joined: 14 Aug 2006
Posts: 4228
Location: London,
United Kingdom
Thanked: 347 times

PostPosted: Tue Oct 11, 2011 9:33 am Reply with quote

compheat wrote:
Rob wrote:
Red and yellow alternating would indicate faulty pressure switch.


A and B flashing (both red) alternately idictate a pressure problem.
I didn't realise that both the red and yellow lights flashed.

A=Red
B=Red both fault lights
C= burner lit
D= power on


The Cb28 only has two LEDs icon_wink.gif
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52905
Location: London,
United Kingdom
Thanked: 3331 times

PostPosted: Tue Oct 11, 2011 9:54 am Reply with quote

But a single LED can be bi or tri colour.

By varying the power to each individual colour a wide range of colours can be produced. As used on LED television displays.
Back to top
 Alert Moderators
lisa31

from United Kingdom

Joined: 13 Apr 2011
Posts: 15
Location: United Kingdom

PostPosted: Tue Oct 11, 2011 11:28 am Reply with quote

I increased the pressure and it still cut out, and it does only have 2 LED lights and have only ever seen red and yellow, never any other colour, the manual also says it only has red/yellow neon lights. I think i would prefer to buy a new part rather than bend or mess with the one that is already there as im not ready to die yet ha ha.
Back to top
 Alert Moderators
DP

from United Kingdom

Joined: 10 Dec 2003
Posts: 6503
Location: Glasgow,
United Kingdom
Thanked: 747 times

PostPosted: Tue Oct 11, 2011 11:49 am Reply with quote

Quote:
But a single LED can be bi or tri colour.


Not on this boiler Tony.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Intermittent Hot Water Alpha CB28 3 680 Thu Mar 27, 2008 8:55 pm
Alpha CB24/CB28 Hot Water Issue 17 12840 Mon Feb 13, 2006 9:41 pm
Alpha cb28 - heating working ok but water not very hot 2 340 Wed Jan 13, 2010 3:04 pm
Alpha CB28 Combi - Luke warm water 7 1020 Tue Jun 24, 2008 7:57 pm
Alpha CB28 no hot water or central heating 14 3720 Thu Mar 18, 2010 1:32 pm


 