PostPosted: Tue Dec 27, 2011 1:46 pm Reply with quote

I've a fault with my Britony SE100

Once the hot tap has been turned off, the boiler appears to stay in hot water mode (the LED light sequence continues as per DHW demand). Boiler is firing, but there's no flow to the taps as they are turned off, but the CH is then heated. The CH is not on (i.e. no demand from thermostat).

If I reset the boiler, the fault stops - i.e. boiler goes to ready state. However the fault has recurred.

From the little I know, I guess this is something to do with the three way valve, the diaphram (?), and or the DHW flow switch.

Supplementary - when I replace this heap in the spring, what should I get instead ?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
boilerbeasty

from United Kingdom

Joined: 14 Jan 2004
Posts: 177
Location: United Kingdom
Thanked: 5 times

PostPosted: Tue Dec 27, 2011 4:03 pm Reply with quote

So taking a closer look, the microswitch looks OK, and is actuated properly when the hot tap is run. However there seems to be some rusty sludge inside the body of this thing - which you can see into through the gap.



I guess the sludge is damping the mechanism- it may have been gumming up the microswitch just enough before I cleaned it a little.

I'm not sure where the leak is coming from or how to fix it. Can someone give me a hint ?

Thanks
Back to top
 Alert Moderators
ihatemyjob

from United Kingdom

Joined: 07 Jan 2010
Posts: 931
Location: Surrey,
United Kingdom
Thanked: 217 times

PostPosted: Tue Dec 27, 2011 7:33 pm Reply with quote

If youre losing pressure the leak is likely to be from the diverter valve,if yore not losing pressure it will be the diaphragm housing.The cartridge in the 3 way valve can be changed quite easily,as can diaphragm housing.
Back to top
The following user says thank you to ihatemyjob for this useful post:
boilerbeasty (30 Dec 2011)
 Alert Moderators
boilerbeasty

from United Kingdom

Joined: 14 Jan 2004
Posts: 177
Location: United Kingdom
Thanked: 5 times

PostPosted: Tue Dec 27, 2011 7:57 pm Reply with quote

Its losing pressure gradually - its been leaking for about a month and needed topping up about once a week.

From what you said, this means its the diverter valve. How do I go about fixing this ? I haven't taken it apart yet (apart from removing the microswitch to clean it up and have a look) so the innards are a mystery to me at the moment !
Back to top
 Alert Moderators
boilerbeasty

from United Kingdom

Joined: 14 Jan 2004
Posts: 177
Location: United Kingdom
Thanked: 5 times

PostPosted: Tue Dec 27, 2011 9:12 pm Reply with quote

Ah OK a bit more digging and I have found the exploded parts view of these boilers.

http://www.aroundtownflats.com/manuals/Boilers/Chaffoteaux/britony%20se%20spare%20parts%20list%202002%20-%20on.pdf

I assume the cartridge is the valve assembly which sits below the diaphragm on page 157.


[/url]
Back to top
 Alert Moderators
ihatemyjob

from United Kingdom

Joined: 07 Jan 2010
Posts: 931
Location: Surrey,
United Kingdom
Thanked: 217 times

PostPosted: Wed Dec 28, 2011 8:28 pm Reply with quote

Key number 509,drain boiler,turn off cold inlet,remove diaphragm housing(2 clips,1 below microswitch,1 on the left of dia/housing)valve cartridge is removed by twisting anti clockwise&pulling up at same time,a sort of bayonet type fixing.You may also need a new microswitch if this is sticking&causing boiler to stay on.
Back to top
 Alert Moderators
boilerbeasty

from United Kingdom

Joined: 14 Jan 2004
Posts: 177
Location: United Kingdom
Thanked: 5 times

PostPosted: Thu Dec 29, 2011 10:11 am Reply with quote

Thanks ihatemyjob, I'll get the parts tomorrow and fix this.

The microswitch did get gummed up and stick a couple of times so I think I will replace it even though I have cleaned it up fairly well. The failure mode when it sticks is potentially disastrous (continuously heating the CH circuit) so I'm not going to risk it.
Back to top
 Alert Moderators
boilerbeasty

from United Kingdom

Joined: 14 Jan 2004
Posts: 177
Location: United Kingdom
Thanked: 5 times

PostPosted: Fri Dec 30, 2011 7:54 pm Reply with quote

Got a new valve and microswitch, retail with next day 12pm delivery total about 40quid.

After isolating everything and draining the CH and DHW as far as possible, I took the motor head off and then the valve head. The valve body was not very easy to turn, and attention to gripping and twisting the right part is needed. Here's a photo for future reference of forum users. The arrow shows the bayonet lug where the valve body locates into the water block, and the body needs gripping and twisting anticlockwise.

This needed a little force.

However no amount of force could persuade the valve body to come up and out of the housing. Different tools, angles of attack and amounts of force were tried for about an hour ! I asked my neighbour who is a professional familiar with this boiler if he could have a go since I didn't want to take the whole water section out. He couldn't get it to budge either and in the end, the whole water section had to come off and the valve body pushed out from the other side, which he very kindly did. As well as having a top bloke for a neighbour, there was also the Christmas miracle of none of the joints leaking when it was put back together !

Thanks to my neighbour and ihatemyjob for the advise and help. Apologies for above detail but its sometimes useful if someone has written up their experiences when searching on some topic.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Britony Combi se 7 340 Sat Feb 14, 2009 7:21 pm
britony combi 80 boiler 5 280 Mon Mar 30, 2009 10:34 am
Britony combi boiler 100 se 7 520 Wed Feb 11, 2009 5:23 pm
Fault on CM Britony 80 Combi Boiler - No CH 6 380 Mon Jan 05, 2009 3:21 pm
C&M Britony Combi Boiler HELP PLEASE 3 160 Thu Dec 11, 2008 3:27 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.