Exotic pilot light problem

Goto page Previous  1, 2, 3, 4  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
palmyra

from United Kingdom

Joined: 08 Oct 2009
Posts: 19
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Oct 09, 2009 8:50 am    Post Subject:
Reply with quote Thanks

Thanks, a couple of silly questions then-
1. ASD ? i can certainly ask him to check it when he turns up with the ordered parts, which may not even apply

2. If there is overheat stat, is it located where the boiler thermostat control box is, which has the capillary going to it? I can't see in manual any reference, except control box plus thermostat with capillary tube and then thermocouple description, as only things that tell the solenoid when to cut off gas.
So if it is overheat stat, would thermostat change cure that, too basically.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24304
Location: London,
United Kingdom
Thanked: 191 times

PostPosted: Fri Oct 09, 2009 11:06 am    Post Subject:
Reply with quote Thanks

You dont seem to have read my answer very well.

IF there is an o/h stat then in the circumstances this may well be causing the pilot to go out.

I explained that my supposition could be checked by powering the pump and turning off the boiler and seeing if it still tripped out.

Depending on how it is wired, that might be achieved just by turning the boiler stat down.

You said the boiler stat makes no difference. That would indicate its faulty. I dont see why you want to change the pilot assembly instead of the thermostat.

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19144
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Fri Oct 09, 2009 11:16 am    Post Subject:
Reply with quote Thanks


__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24304
Location: London,
United Kingdom
Thanked: 191 times

PostPosted: Fri Oct 09, 2009 11:49 am    Post Subject:
Reply with quote Thanks

Kev, a copy of the page showing 10.5 with the optional o/h stat might help him.

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19144
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Fri Oct 09, 2009 12:18 pm    Post Subject:
Reply with quote Thanks

your wish oh great one



is my command icon_wink.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19144
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Fri Oct 09, 2009 12:19 pm    Post Subject:
Reply with quote Thanks

delete please icon_redface.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
holty

from United Kingdom

Joined: 14 Jan 2006
Posts: 1343
Location: Cornwall,
United Kingdom
Thanked: 21 times

PostPosted: Fri Oct 09, 2009 12:20 pm    Post Subject:
Reply with quote Thanks

think your both having a mix up. the drawings and type boiler your refering to is the 45/4. were as the op seems to have the 45/2. totally different inners. ones permanent pilot the other aint.
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19144
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Fri Oct 09, 2009 12:23 pm    Post Subject:
Reply with quote Thanks

cheers holty icon_redface.gif

ain't got a book on that one

if anybody has adress in profile icon_wink.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
holty

from United Kingdom

Joined: 14 Jan 2006
Posts: 1343
Location: Cornwall,
United Kingdom
Thanked: 21 times

PostPosted: Fri Oct 09, 2009 12:25 pm    Post Subject:
Reply with quote Thanks

ill try send one asap
Back to top
The following user says thank you to holty for this useful post:
kevplumb (9 Oct)
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19144
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Fri Oct 09, 2009 12:27 pm    Post Subject:
Reply with quote Thanks

thanks fella icon_wink.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
holty

from United Kingdom

Joined: 14 Jan 2006
Posts: 1343
Location: Cornwall,
United Kingdom
Thanked: 21 times

PostPosted: Fri Oct 09, 2009 12:30 pm    Post Subject:
Reply with quote Thanks

sent, hopefully icon_smile.gif
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19144
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Fri Oct 09, 2009 12:38 pm    Post Subject:
Reply with quote Thanks

thanks icon_biggrin.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
palmyra

from United Kingdom

Joined: 08 Oct 2009
Posts: 19
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Oct 09, 2009 12:48 pm    Post Subject:
Reply with quote Thanks

many thanks, this should be enough ammunition to change his mind from going through thermocouple change which was initial theory. He'll bring probably the ordered part, doesn't hurt to have one spare , but as long as the temperature dependence is clear clue for stat-related look first, I might save some tedium.
Anyway will come back with update, hopefully soon I get a slot booked in with him. Kinda catch 22, because he's gating it by arrival of his ordered thermocouple icon_sad.gif
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19144
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Fri Oct 09, 2009 12:52 pm    Post Subject:
Reply with quote Thanks

tell him to check the filter on the asd as well

now we are all talking about the same boiler icon_redface.gif (thanks holty)

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
palmyra

from United Kingdom

Joined: 08 Oct 2009
Posts: 19
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Oct 09, 2009 4:11 pm    Post Subject:
Reply with quote Thanks

thanks again and quite in awe of the erudite chat -
Indeed, mine has basically only two thin metal tubes coming out from the pilot light under the viewing window, both touch the chassis (not sure if relevant, although chassis does get hot after a long burn).

Then no trace of any separate overheat sensor from what I can see (also on my schematic), except the separate thermostat control box where the mains cable comes in, this box has the capillary going in from the boiler.

So then the boiler thermostat may be leading to the decision of cutting everything off, certainly as you remarked, makes no difference to radiator temperature either.

It's quite a 'dumb' boiler in that sense that on the Glow Worm manual nor what I saw during the recent servicing had any other sensor at least from what I could see and/or hunt down in the manual.

Will be quite interesting, once I do get finally a solid booking - even considered buying a thermostat unit which seems quite cheap, so that I can present it to him and just ask to try it while at it, he will have to disassemble the entire thing anyway. Still better than another N bookings 'til Xmas icon_smile.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page Previous  1, 2, 3, 4  Next
Page 2 of 4

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
neptune exotic shower problem 5 380 Mon Jan 01, 2007 10:32 pm
Potterton Puma 80 Pilot Light Problem 2 360 Mon Dec 31, 2007 5:44 pm
Pilot Light Problem 2 1760 Sun Feb 05, 2006 6:19 pm
Glow-worm spacesaver 38 pilot light problem 4 580 Mon Mar 19, 2007 9:12 am
baxi boiler pilot light problem 4 240 Fri Jul 25, 2008 11:56 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.