Hi,
My FIL has a 30 yr old Trianco boiler Redfyre TRO,basically it runs for 5-6 mins then cuts out, any ideas apart from buying a new boiler would be great
thanks
Joined: 10 Jun 2009 Posts: 575 Location: Suffolk, United Kingdom Thanked: 53 times
Posted: Fri Oct 09, 2009 6:45 pm Post Subject:
Trianco have fitted many diffrent burners over the years, but i suspect yours will be an E.O.G.B. inter burner, i suspect that the Solenoid Coil is faulty, (going open circuit when hot) BUT! check the fuel supply to the burner is not resticted by closed valves or blocked filters first.
Joined: 16 Sep 2003 Posts: 7790 Location: United Kingdom Thanked: 7 times
Posted: Sat Oct 10, 2009 5:09 am Post Subject:
I agree, solenoid coil is the likely cause. Though with a boiler that age, FIL should be saving up for a replacement (even though it may last several years yet).
Joined: 09 Oct 2009 Posts: 4 Location: Oxfordshire, United Kingdom Thanked: 0 times
Posted: Sat Oct 10, 2009 7:23 pm Post Subject:
model
hello,
thanks all for the replies, my fil cant seem to find a model number, is there somewhere inside it that wll tell him?also where do we get spare parts for such an old boiler?
thanks
again
Joined: 16 Sep 2003 Posts: 7790 Location: United Kingdom Thanked: 7 times
Posted: Sun Oct 11, 2009 10:41 am Post Subject:
Inside the boiler you will see the burner, black or orange I expect. On one side is the motor, on the other is the oil pump, made by Danfoss. The pump has a model name on it, MSLA if it's an old pump, BFP if it's newer. Just look for a coil to suit, though it would be wise to check the coil resistance immetiately the boiler locks out. Expect to pay up to £40 for a coil.
Joined: 09 Oct 2009 Posts: 4 Location: Oxfordshire, United Kingdom Thanked: 0 times
Posted: Fri Oct 16, 2009 7:27 pm Post Subject:
Another question-Control unit
Hello,
My fil has basically bought a new solenoid, filter, light sensor thing!! and a new control box, the original was a danfoss bh011.1 with a replacement being a bh072.10, the wiring is a little differant, on the old box the photo cell is connected to term 2 i think what terminal s on the new box do i connect the photo cell to???also when the control box is removed and the wires bridged it runs ok but cuts out after 5 secounds of firing up
thanks
shaun