The Rayburn and its S plan

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 668
Location: Northumberland,
United Kingdom
Thanked: 52 times

PostPosted: Wed Nov 04, 2009 4:51 pm    Post Subject:
The Rayburn and its S plan
Reply with quote Thanks

Continuing to be haunted by this heating system, I've now put a new ST6400c programmer on, and all seems to be well. I'm now trying to balance the system - which I think is a S plan (2 MV's in loft, 1 pump, cylinder stat and room stat).
However, the HW header tanks have an expansion pipe, but the F&E tank does not, and if most of the rads are closed off, hot water bubbles up the flow pipe of the F&E until the boiler shuts down.
Is this in order? I'm confused even more now? Comments please?
Thanks John icon_smile.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 668
Location: Northumberland,
United Kingdom
Thanked: 52 times

PostPosted: Thu Nov 05, 2009 10:03 am    Post Subject:
Reply with quote Thanks

Please, any comments, gents? icon_smile.gif
Back to top
 Alert Moderators
twgas

from United Kingdom

Joined: 26 Oct 2007
Posts: 2145
Location: Kent,
United Kingdom
Thanked: 41 times

PostPosted: Thu Nov 05, 2009 10:44 am    Post Subject:
Reply with quote Thanks

How pold is it and has it ever worked properly?
Where does the cold feed join the system?
I would think there should be a vent on an aga - check MIs or ring Aga.

__________________
Death can be fatal !!!!!!!
Mick.
Back to top
The following user says thank you to twgas for this useful post:
Burnerman (5 Nov)
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19164
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Thu Nov 05, 2009 10:50 am    Post Subject:
Reply with quote Thanks

burnerman wrote:
However, the HW header tanks have an expansion pipe, but the F&E tank does not, and if most of the rads are closed off, hot water bubbles up the flow pipe of the F&E until the boiler shuts down.



lack of a bypass icon_idea.gif

__________________
a little thanks

goes a long way
Back to top
The following user says thank you to kevplumb for this useful post:
Burnerman (5 Nov)
 Alert Moderators
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 668
Location: Northumberland,
United Kingdom
Thanked: 52 times

PostPosted: Thu Nov 05, 2009 11:18 am    Post Subject:
Reply with quote Thanks

twgas wrote:
How pold is it and has it ever worked properly?
Where does the cold feed join the system?
I would think there should be a vent on an aga - check MIs or ring Aga.


The Rayburn in question is 1999 - I don't know if it has ever worked properly. The property is a bungalow - the boiler feed / return pipes go into the loft where there are 2 MV's and the copper cylinder, plus header and F&E tanks. The pipes then descend back to the underfloor where they feed the rads. The system does work reasonably - at least all of the rads heat up eventually - I'm trying to balance things so they all reach similar temperatures. However most of the rads have TRV's and I feel, when the tenants get in, they will turn some of them off which results in momentary boiling until the boiler shuts things off. Hence my concern about the lack of expansion pipe.
Thanks for your reply - much appreciated! Cheers John icon_smile.gif
Back to top
 Alert Moderators
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 668
Location: Northumberland,
United Kingdom
Thanked: 52 times

PostPosted: Thu Nov 05, 2009 11:22 am    Post Subject:
Reply with quote Thanks

kevplumb wrote:
burnerman wrote:
However, the HW header tanks have an expansion pipe, but the F&E tank does not, and if most of the rads are closed off, hot water bubbles up the flow pipe of the F&E until the boiler shuts down.



lack of a bypass icon_idea.gif


Kev, I don't know if there is a bypass fitted, but I appreciate that there should be...I have a feeling that one of the bathroom radiators may be acting as one, but again they have TRV's fitted icon_confused.gif I can't access the main flow and return pipes - they are buried under a timber floor which has quarry tiles on it icon_sad.gif Anyway the system seems calm so long as the boiler stat isn't put too high, and the rad TRV's are left open. I'm closing them down one at a time to see if the boiler overheats.
Thanks for your reply - much appreciated. Cheers John icon_smile.gif
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Thu Nov 05, 2009 11:31 am    Post Subject:
Reply with quote Thanks

I know that some of you seem hell bent on nightmare jobs!

However, as this is for a landlord then its a potential double nightmare.

I just dont see how you can ever charge for the work you would have to do to understand it.

Just fitting an auto bypass should sort it out. Why not just do that and forget how its configured?

Tony

__________________
ARGI Registered Engineer
Back to top
The following user says thank you to Agile for this useful post:
Burnerman (5 Nov)
 Alert Moderators
twgas

from United Kingdom

Joined: 26 Oct 2007
Posts: 2145
Location: Kent,
United Kingdom
Thanked: 41 times

PostPosted: Thu Nov 05, 2009 11:33 am    Post Subject:
Reply with quote Thanks

Is the pump also in the loft? If so then it's just a question of looking to see if there are any tees between the pump and mvs, and see where it/they go.

__________________
Death can be fatal !!!!!!!
Mick.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Thu Nov 05, 2009 11:37 am    Post Subject:
Reply with quote Thanks

Does anyone remember the fellow who installed a second hand range for a lady?

She refused to pay for 28 mm heating pipes so he did it in 22 and it overheated.

She reported him to CORGI who found he was working out of scope. Instead of rushing out to take the assessment he did nothing! They agreed that he would replace the heating pipe in 28 mm and she was to have paid just for the materials.

He replaced the pipes but it still did not work properly and she never paid anything more but instead sued him for £3300 !

I never heard the outcome but thats an example of someone who takes on a difficult job with a difficult customer and ends up seriously out of pocket.

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
picasso

from United Kingdom

Joined: 08 Apr 2008
Posts: 506
Location: Essex,
United Kingdom
Thanked: 70 times

PostPosted: Thu Nov 05, 2009 11:58 am    Post Subject:
Reply with quote Thanks

which model of rayburn is it ?
Back to top
 Alert Moderators
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 668
Location: Northumberland,
United Kingdom
Thanked: 52 times

PostPosted: Thu Nov 05, 2009 1:35 pm    Post Subject:
Reply with quote Thanks

picasso wrote:
which model of rayburn is it ?


Its a 499k, twin Nu Way burner with soft start. icon_smile.gif
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19164
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Thu Nov 05, 2009 1:38 pm    Post Subject:
Reply with quote Thanks

Quote:
twin Nu Way burner with soft start.


bet your head is on soft start after this icon_lol.gif icon_lol.gif icon_wink.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 668
Location: Northumberland,
United Kingdom
Thanked: 52 times

PostPosted: Thu Nov 05, 2009 1:39 pm    Post Subject:
Reply with quote Thanks

Agile wrote:
I know that some of you seem hell bent on nightmare jobs!

However, as this is for a landlord then its a potential double nightmare.

I just dont see how you can ever charge for the work you would have to do to understand it.

Just fitting an auto bypass should sort it out. Why not just do that and forget how its configured?

Tony


The owners are actually friends of mine - so far icon_lol.gif and I'm trying to do them a favour....
Tony, please tell me about an auto bypass, and if it can be fitted even if there could be a radiator acting as one? Bearing in mind I cannot access any of the flow and return pipes apart from where they are in the loft, which is at least 15 feet from the Rayburn. Cheers John icon_smile.gif
Back to top
 Alert Moderators
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 668
Location: Northumberland,
United Kingdom
Thanked: 52 times

PostPosted: Thu Nov 05, 2009 1:40 pm    Post Subject:
Reply with quote Thanks

kevplumb wrote:
Quote:
twin Nu Way burner with soft start.


bet your head is on soft start after this icon_lol.gif icon_lol.gif icon_wink.gif


icon_biggrin.gif icon_biggrin.gif made my day! John icon_smile.gif
Back to top
 Alert Moderators
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 668
Location: Northumberland,
United Kingdom
Thanked: 52 times

PostPosted: Thu Nov 05, 2009 1:41 pm    Post Subject:
Reply with quote Thanks

twgas wrote:
Is the pump also in the loft? If so then it's just a question of looking to see if there are any tees between the pump and mvs, and see where it/they go.


Yes thanks.....if the thing overheats again its time to call out the artillery icon_smile.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
OUR OLD RAYBURN 5 220 Sun Aug 30, 2009 11:21 pm
Controlling DHW from Rayburn 2 100 Sun Jul 26, 2009 9:21 pm
Rayburn question 2 160 Mon Jul 06, 2009 6:43 pm
Hot water valves from Rayburn boiler 6 220 Sun May 17, 2009 4:00 pm
Overheating Rayburn? 5 220 Thu Sep 24, 2009 6:04 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.