lostforwords

from United Kingdom

Joined: 03 Nov 2009
Posts: 12
Location: Nottinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Nov 03, 2009 9:13 pm    Post Subject:
Reply with quote Thanks

Norcon

I am with you on that!!

BUT (the big but) the Builder seems to think all is ok and I should take the matter to NHBC (he seems far to relaxed and hence why I raise the question).

If the Approved Document is just "guidance" and you can use alternative methods to achive the same PERFORMANCE how do you go about arguing the case.

I am aware that the Building Act actually states that for Court matters that not following the Approved Documents tends to presume non compliance (up to Builder to prove otherwise in this arena).

My other problem is that NHBC also did the Building Control, however they do not appearto have any records of what was inspected !!!!! Is it right for them to have a presumption of compliance ? Can they pass the drains on the plans alone ? What if the drains dont match the plans? The list is endless.

Just trying to ensure I dont end up with duff drainage that seriously devalues the house.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
lostforwords

from United Kingdom

Joined: 03 Nov 2009
Posts: 12
Location: Nottinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Nov 03, 2009 9:17 pm    Post Subject:
Reply with quote Thanks

Picasso

My drawing is the other way round to the photo.

To clarify on the photo the horizontal flow would be from left to right (normally!)

I actually think the T is in totally the wrong position.........it should not feature!
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19149
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Tue Nov 03, 2009 9:21 pm    Post Subject:
Reply with quote Thanks

Quote:
If the Approved Document is just "guidance" and you can use alternative methods to achive the same PERFORMANCE how do you go about arguing the case.


well if it ain't working it isn't acheiving it is a good starting point icon_idea.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
picasso

from United Kingdom

Joined: 08 Apr 2008
Posts: 500
Location: Essex,
United Kingdom
Thanked: 66 times

PostPosted: Tue Nov 03, 2009 9:27 pm    Post Subject:
Reply with quote Thanks

many years ago I was working on a site with another plumber , he was doing the general plumbing and I was doing the heating, after a visit from building control the stacks had to be changed as the plumber had used a short radius 90 bend, it had to be changed to a long radius bend with foot (think they are called rest bends) it sounds like nhbc and your builder have dropped a **** and are trying to talk their way out of it.
Back to top
The following user says thank you to picasso for this useful post:
lostforwords (3 Nov)
 Alert Moderators
lostforwords

from United Kingdom

Joined: 03 Nov 2009
Posts: 12
Location: Nottinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Nov 03, 2009 9:39 pm    Post Subject:
Reply with quote Thanks

Picasso

I agree. If Builder disagrees then you take them to NHBC under their "dispute resolution Service".......If NHBC also did the Building Control and missed the point, it somehow seems to be a loaded dice !

Will NHBC rule that their Approved Inspectors ****** up !
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Tue Nov 03, 2009 10:25 pm    Post Subject:
Reply with quote Thanks

I would write a nice letter to the builder and the NHBC, explaining that something is clearly wrong to be getting the backup of waste products in the waste pipe.

I would give them say 14days to sort, or you be hiring a consultant and your own builder at the builders expense to get the drains re-laid, you may want to mention a four figure sum for compensation whilst you're at it.
Back to top
 Alert Moderators
Hugh Jaleak

from United Kingdom

Joined: 03 Feb 2008
Posts: 423
Location: Northamptonshire,
United Kingdom
Thanked: 28 times

PostPosted: Tue Nov 03, 2009 11:04 pm    Post Subject:
Reply with quote Thanks

Builder will be relaxed, he's sold the house, why should he worry? !!! He's not got the smell problems, and is probably confident he wont have to spend money sorting out anything major now! I have heard of the NHBC can sometimes be a 'closed shop', run by builders for builders, rather akin to the GMC for doctors, so I wouldnt hold my breath with them....

May be worth having a chat with Building Control at your local council. BCO should be able to advise if the arrangement you have is acceptable, although I'd be surprised if it is. Building regs state use of long radius bend, at that to me is basically the required standard of workmanship and design for buildings in this country, failure to do so can result in the works having to be redone to standard. However, BCO cannot inspect every property at every stage on every development.

If the BCO is prepared to come onside and isnt happy with the arrangement, then you could gain some decent ammo to fire at the builder and NHBC. If there have been a few built, all with this design flaw in the drains then im sure the builder wont want too much fuss making in case he ends up fixing the lot!
Back to top
 Alert Moderators
lostforwords

from United Kingdom

Joined: 03 Nov 2009
Posts: 12
Location: Nottinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 05, 2009 2:38 pm    Post Subject:
Reply with quote Thanks

Interesting Post Script

Have done a little more research into Building Regs etc. Section 7 of the Building Act 1984 basically states that in civil (or criminal) proceedings, compliance with the approved documents suggests no liability and non-compliance suggests liability where non compliance with the Building Regulations is an issue.

Therefore up to builder to explain his way out of things if it gets to Court (and of course why should I settle for anything less on the way knowing I have the above to assist me ! icon_twisted.gif
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Thu Nov 05, 2009 4:29 pm    Post Subject:
Reply with quote Thanks

The only way you can prove non-compliance is to get an independent to excavate the pipe, and physically check how it's installed.

Hence the need for a recorded letter to the builder, giving them the opportunity to rectify any problem, and of your intent if it's not done in X days.
Back to top
The following user says thank you to doitall for this useful post:
lostforwords (5 Nov)
 Alert Moderators
lostforwords

from United Kingdom

Joined: 03 Nov 2009
Posts: 12
Location: Nottinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 05, 2009 5:16 pm    Post Subject:
Reply with quote Thanks

Doitall

I think I have all the evidence I need from a CCTV survey from inside the pipe!
Back to top
 Alert Moderators
Hugh Jaleak

from United Kingdom

Joined: 03 Feb 2008
Posts: 423
Location: Northamptonshire,
United Kingdom
Thanked: 28 times

PostPosted: Thu Nov 05, 2009 5:28 pm    Post Subject:
Reply with quote Thanks

I think the onus would be on you then to prove the CCTV footage was of the pipe under your house if this got to court. Id agree with DIA, it needs a written assessment, possibly backed up by photographs, from a drainage engineer as to the situation. The court would likely need a clear explanation of the appropriate building regs, they have to make a decision based on the evidence in front of them, you need to present a good case if it went this far.....

The builder may have a good solicitor so be prepared!
Back to top
The following user says thank you to Hugh Jaleak for this useful post:
lostforwords (5 Nov)
 Alert Moderators
Nige F

from United Kingdom

Joined: 28 Jun 2005
Posts: 7494
Location: United Kingdom
Thanked: 31 times

PostPosted: Thu Nov 05, 2009 5:43 pm    Post Subject:
Reply with quote Thanks

He may have a good solicitor, he sure as hell aint got any good drainlayers. icon_rolleyes.gif That`s the way it`s all going today. Masses of paper+ Health safety and so on . Not 1 decent 2 x"O " Level Plumber/ drainlayer for frigging miles icon_lol.gif All gone Gas safe or retired.
Back to top
The following user says thank you to Nige F for this useful post:
lostforwords (5 Nov)
 Alert Moderators
lostforwords

from United Kingdom

Joined: 03 Nov 2009
Posts: 12
Location: Nottinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 05, 2009 5:52 pm    Post Subject:
Reply with quote Thanks

I have a CCTV Survey and can have my engineer confirm it is our property, also Builder has had two surveys undertaken and has the video so that will conclusively prove what is at the location. Any argument and yet another survey can be undertaken.

NHBC can ask for tests and investigations to be done - so I can use this to gather yet more evidence if they will play ball !

THE CCTV shows no rest bend at bottom of stack, therefore Approved Document not followed, then up to Builder to prove it complies and not for me to prove any further. The Building act really says the builder wants to deviate from the guidance in the approved document he will need to prove his innocence rather than for the houseowner to prove guilt.

In view of facts (the present system can't get anywhere near that in the guidance) and the above a skillful solicitor would hopefully advise his client to sort the thing out rather than to risk the addition of my legal costs as well.
Back to top
 Alert Moderators
Hugh Jaleak

from United Kingdom

Joined: 03 Feb 2008
Posts: 423
Location: Northamptonshire,
United Kingdom
Thanked: 28 times

PostPosted: Thu Nov 05, 2009 6:00 pm    Post Subject:
Reply with quote Thanks

Best of luck with it lostforwords. Its not a satisfactory situation, at best unsanitary, at worst liable to block repeatedly over time. I do wonder where modern groundworkers learn drainlaying, like Nige F said, its more about having a piece of paper to say you've been on a safety course than what you actually know about doing the job I think..... icon_confused.gif

Years ago the sanitary inspector used to test drain runs by rolling a ball down, I wonder how many would pass that test today.....
Back to top
 Alert Moderators
Norcon

from United Kingdom

Joined: 17 May 2008
Posts: 1037
Location: United Kingdom
Thanked: 17 times

PostPosted: Thu Nov 05, 2009 6:22 pm    Post Subject:
Reply with quote Thanks

Not thats its relevant but building site I'm on at the moment (large nursing home) has pipes laid this week in a similar fashion to the Op's.
Extensive ground work is ongoing.
Might ask the builder tomorrow if they are soil pipes. (not that its any of my business)
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page Previous  1, 2
Page 2 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Building Regs advice needed - soil stack 3 880 Mon Aug 01, 2005 8:11 pm
One for the Building Regs gurus 3 240 Mon Mar 17, 2008 10:42 pm
PolyPipe buried in Screed and Building Regs 3 200 Wed Aug 27, 2008 9:35 pm
max 4'' waste run contravening old building regs?? 2 260 Tue Feb 12, 2008 2:11 am
Building Regs - min distance between gas/elec/water 3 160 Tue Oct 13, 2009 3:53 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.