Worcester 40 CDi - Fault

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
lufcmark

from United Kingdom

Joined: 31 May 2009
Posts: 23
Location: United Kingdom
Thanked: 1 time

PostPosted: Wed Nov 04, 2009 9:45 pm    Post Subject:
Worcester 40 CDi - Fault
Reply with quote Thanks

Evening all...Bit long winded this, i'll be as brief as possible.

Recently installed 40CDi on an existing powerflushed open vented system, 28mm boiler F&R to pump & controls approx 6m from boiler. On demand boiler fires briefly (2-3secs) before displaying a hydraulic fault symbol (opposite corners flashing on and off with flow temp). This mode begins with the flow temp as low as 22deg and continues for approx 45mins at which point the boiler usually fires up properly...Worcs came out and ok'd the appliance and pointed the finger at the pump, we upgraded the pump from a 15/60 to a 25/55 and problem persists on all 3 pump speed settings. When boiler is in high fire all 25 rads kick in nicely and I am as sure as I can be that there is not a circulation problem.

No other error codes are being displayed and all I am getting from Worcs Tech is "...it's not a boiler fault..."

Any thoughts would be gratefully recieved, thanks in advance Mark.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10121
Location: London,
United Kingdom
Thanked: 188 times

PostPosted: Wed Nov 04, 2009 11:47 pm    Post Subject:
Reply with quote Thanks

Bit of debris ended up near pump or boiler blocking the flow?

__________________
Don't feed the troll.
Back to top
 Alert Moderators
APHSLTD

from United Kingdom

Joined: 05 Feb 2009
Posts: 90
Location: Aberdeen,
United Kingdom
Thanked: 13 times

PostPosted: Thu Nov 05, 2009 12:05 am    Post Subject:
Re: Worcester 40 CDi - Fault
Reply with quote Thanks

lufcmark wrote:
Evening all...Bit long winded this, i'll be as brief as possible.

Recently installed 40CDi on an existing powerflushed open vented system, 28mm boiler F&R to pump & controls approx 6m from boiler. On demand boiler fires briefly (2-3secs) before displaying a hydraulic fault symbol (opposite corners flashing on and off with flow temp). This mode begins with the flow temp as low as 22deg and continues for approx 45mins at which point the boiler usually fires up properly...Worcs came out and ok'd the appliance and pointed the finger at the pump, we upgraded the pump from a 15/60 to a 25/55 and problem persists on all 3 pump speed settings. When boiler is in high fire all 25 rads kick in nicely and I am as sure as I can be that there is not a circulation problem.

No other error codes are being displayed and all I am getting from Worcs Tech is "...it's not a boiler fault..."

Any thoughts would be gratefully recieved, thanks in advance Mark.


The fault you are describing is the gradiant limitation kicking in, boiler flow temp is rising to quickly.

How is your system set up? is the heating split into zones? is it two or three port zone valves that are used? Is there a system by-pass fitted?
Back to top
The following user says thank you to APHSLTD for this useful post:
lufcmark (5 Nov)
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24307
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Thu Nov 05, 2009 12:22 am    Post Subject:
Reply with quote Thanks

While you are here, whats the official name and cause of the [ ] symbol?

Are you in the CC yet?
Back to top
 Alert Moderators
APHSLTD

from United Kingdom

Joined: 05 Feb 2009
Posts: 90
Location: Aberdeen,
United Kingdom
Thanked: 13 times

PostPosted: Thu Nov 05, 2009 9:19 am    Post Subject:
Reply with quote Thanks

Agile wrote:
While you are here, whats the official name and cause of the [ ] symbol?

Are you in the CC yet?


That symbol is the syphon-fill Tony. When the boiler fires from new it first goes through an 8 minute air purge as there is no AAV on the heat exchanger. This is a one time only function however it can be turned on in service mode if required.

After that the boiler then goes into syphon-fill where it fires at low rate for 15mins to fill the trap.

every time power is interupted to the boiler ie spur or on off switch are switched off but not after boiler re-set it will go through syphon-fill before returning to normal operation.

That is not the symbol he is describing though, the symol he is describing is similar, [] imagine that but cut in half on the top left you have half that symbol and on the bottom right you have half that symbol.

I suspect it's low flow on start up or boiler needs to be rated.

And yes I have made it to the CC icon_lol.gif
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24307
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Thu Nov 05, 2009 11:11 am    Post Subject:
Reply with quote Thanks

Neither of those symbols are shown in the MI that comes with the boiler on the R40 that I was looking at yesterday.

Is there a "better" version of the MIs that I could ask for with all the information in it?

Tony.

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
lufcmark

from United Kingdom

Joined: 31 May 2009
Posts: 23
Location: United Kingdom
Thanked: 1 time

PostPosted: Thu Nov 05, 2009 5:52 pm    Post Subject:
Reply with quote Thanks

The system is set up as follows: Grundfos 25/55, 22mm auto by-pass and then 3no. 22mm 2 port valves, one for the HW and the other two for the two 22mm heating circuits. Although there are two 22mm heating circuits they act as one zone and the two 22mm heating zone valves operate simultaneously.

When I set the boiler to max via the boost button it takes 7 minutes for the flow temp to rise from 30deg to 70deg (fault symbol still displayed during this mode).

The system only needs about 35kw but when I suggested down rating the boiler to the Worcs Tech bloke he didn't seem over impressed.

Thanks again Mark
Back to top
 Alert Moderators
holty

from United Kingdom

Joined: 14 Jan 2006
Posts: 1343
Location: Cornwall,
United Kingdom
Thanked: 21 times

PostPosted: Thu Nov 05, 2009 7:26 pm    Post Subject:
Reply with quote Thanks

Back to top
The following user says thank you to holty for this useful post:
lufcmark (5 Nov)
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10121
Location: London,
United Kingdom
Thanked: 188 times

PostPosted: Thu Nov 05, 2009 8:46 pm    Post Subject:
Reply with quote Thanks

lufcmark wrote:

When I set the boiler to max via the boost button it takes 7 minutes for the flow temp to rise from 30deg to 70deg

That does not sound right.
What is the total output of the rads roughly?
If you allocate an average of 10L per kW for rads plus pipework, it should take around 25 minutes to go form 30C to 70C.

__________________
Don't feed the troll.
Back to top
 Alert Moderators
lufcmark

from United Kingdom

Joined: 31 May 2009
Posts: 23
Location: United Kingdom
Thanked: 1 time

PostPosted: Thu Nov 05, 2009 8:55 pm    Post Subject:
Reply with quote Thanks

Evening bengasman...total output of rads is 29kw
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10121
Location: London,
United Kingdom
Thanked: 188 times

PostPosted: Thu Nov 05, 2009 9:22 pm    Post Subject:
Reply with quote Thanks

lufcmark wrote:
Evening bengasman...total output of rads is 29kw

30CDI would have done nicely methinks, but never mind, the 40 is there now.

40 kW capacity heats about 14 litres of water 40 degrees in 1 minute. That would lead to 100 litres in 7 minutes if I have my tables right, IF no heat was lost. As there clearly is heat dissipating through the rads, you are left with an estimated 80 - 90 litres that would have been heated up 40 degrees whilst circulating through the rads. Ball park figures obviously. I don't see how 29 kW worth of rads plus the pipework for it could be as little as that.
Q1: did ALL the rads get FULLY hot in that 7 minute span?
Q2: did you gasrate the boiler?
Q3: were all the lockshields wide open?
Q4: was the dhw side closed?
Q5: why didn't you post this in the CC?
Q6: why did you stick a 40kW boiler in on 29 kW of rads?
Q7: did you adjust the rad output to steamer settings?

__________________
Don't feed the troll.
Back to top
 Alert Moderators
lufcmark

from United Kingdom

Joined: 31 May 2009
Posts: 23
Location: United Kingdom
Thanked: 1 time

PostPosted: Thu Nov 05, 2009 10:28 pm    Post Subject:
Reply with quote Thanks

Q1: did all rads get fully hot in that 7min span?
A1: I was concentrating on timing the temp rise so I didn't check.
Q2: did you gas rate the boiler?
A2: 43kw net
Q3: were all the lockshields wide open
A3: no - some, not many, have been turned down.
Q4: was he dhw side closed?
A4: yes
Q5: why didn't you post this in the CC?
A5: wasn't aware of it until now...I assume that this is the CC that Agile was referring to...
Q6: why did you stick a 40kw boiler in on 29kw of rads?
A6: was thinking 29kw heating, 3kw dhw plus 10% for pipe work. Thought I might have been chancing it with the 30 as the client was making a lot of noise about the old boiler not being man enough.
Q7: did you adjust the rad output to steamer settings?
A7: have I got a 20deg differential across the F&R?...no
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10121
Location: London,
United Kingdom
Thanked: 188 times

PostPosted: Thu Nov 05, 2009 10:52 pm    Post Subject:
Reply with quote Thanks

lufcmark wrote:

Q3: were all the lockshields wide open
A3: no - some, not many, have been turned down.

To get rid of the fault "code" during the installation/commisionning, open them relatively wide, e.g. 7-10C drop.

Q6: why did you stick a 40kw boiler in on 29kw of rads?
A6: was thinking 29kw heating, 3kw dhw plus 10% for pipe work.

Modern, high recovery/ high insulation cylinders should be time separate from the ch. They are generally between 10 and 20 kW, so no point adding 3 to the boiler load.
10% for the pipes? icon_confused.gif

Q7: did you adjust the rad output to steamer settings?
A7: have I got a 20deg differential across the F&R?...no


I actually meant if you stuck to the capacity as given by the manufacturer, which is 10 - 15 % more than you actually get on a steamer. In other words: if the table says: 1789 Watt, 1500 - 1600 out of it with a boiler in condensing mode. The result of that would be that the rads that you counted as 29 kW, will only dissipate 25 kW with the new boiler.
It shouldn't be a problem as the boiler will modulate down to about 15 kW.


The boiler is not running too high, so it seems to be a matter of too little flow. Pump is easily big enough, so it must be a restriction somewhere.
Manual bypass somewhere?
"Balance valve" partially shut?
Some numpty that installed a loop?
Limescale/magnetite lump somewhere?

__________________
Don't feed the troll.
Back to top
The following user says thank you to bengasman for this useful post:
lufcmark (6 Nov)
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10121
Location: London,
United Kingdom
Thanked: 188 times

PostPosted: Thu Nov 05, 2009 10:55 pm    Post Subject:
Reply with quote Thanks

Did you check that all the rads are piped properly? All parallel?
Did you clean them all separately with the powerflush?
What chemical did you use?

__________________
Don't feed the troll.
Back to top
 Alert Moderators
lufcmark

from United Kingdom

Joined: 31 May 2009
Posts: 23
Location: United Kingdom
Thanked: 1 time

PostPosted: Thu Nov 05, 2009 11:19 pm    Post Subject:
Reply with quote Thanks

Rads appear to be piped properly albeit in 10mm, not via a common manifold but each teeing into the heating circuit individually...Each rad was flushed seperately and the machine has a pair of magnets so I could see how the flush was going. Used 4 litres of X800.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
worcester 24i rsf ignition fault 6 360 Mon Oct 30, 2006 4:48 pm
Hot water fault with Worcester 25si 4 320 Tue May 13, 2008 1:31 pm
worcester 24i fault? 4 320 Sun Mar 09, 2008 6:05 pm
Worcester Bosch - ZWBR 7-28 HE Plus Hot Water Fault 9 240 Wed Aug 26, 2009 6:22 pm
Worcester 24i fault 7 300 Mon Nov 27, 2006 7:04 pm