NEW BOILER SIZE:

Goto page Previous  1, 2, 3  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Fri Nov 06, 2009 8:06 pm    Post Subject:
Reply with quote Thanks

bengasman wrote:
Second that. Have yet to get a client with less than 100% satisfaction.


How many plate HX have you changed in the last 5 years, or are they better now icon_rolleyes.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 190 times

PostPosted: Fri Nov 06, 2009 8:22 pm    Post Subject:
Reply with quote Thanks

doitall wrote:
bengasman wrote:
Second that. Have yet to get a client with less than 100% satisfaction.


How many plate HX have you changed in the last 5 years, or are they better now icon_rolleyes.gif
Bar 2 exceptions, I have only installed greenstar he + mk2, cdi mk1, and cdi mk2. Had 1 boiler with fried display (due to pulse or lightning according to wb bloke that fixed it foc) and broken lever on diverter, that is all the damage. Never been called out for hex from someone else's install either.

__________________
Don't feed the troll.
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Fri Nov 06, 2009 9:07 pm    Post Subject:
Reply with quote Thanks

Changed at least 10 that had pin holed. and it seems to be quite a common problem.
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 190 times

PostPosted: Fri Nov 06, 2009 9:22 pm    Post Subject:
Reply with quote Thanks

So I heard. Odd, never seen one.
I wonder if it has something to do with how clean the system is.

__________________
Don't feed the troll.
Back to top
 Alert Moderators
Gasman77

from United Kingdom

Joined: 18 Jan 2009
Posts: 99
Location: Berkshire,
United Kingdom
Thanked: 2 times

PostPosted: Fri Nov 06, 2009 10:34 pm    Post Subject:
Reply with quote Thanks

Installed 80-90 WB over the last three years with not one warranty call yet.... Also did a year as a wb engineer and I haven't changed a pin-holed heat ex yet. like I said, installed 2 Avantas, first one lasted an hour, second came with bits missing icon_eek.gif

HQ were less than helpful to be honest.

Maybe i was just unlucky icon_sad.gif
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Fri Nov 06, 2009 10:52 pm    Post Subject:
Reply with quote Thanks

Pretty sure the pin holing plates are something to do with domestic water quality/type so could well be regional.
Back to top
 Alert Moderators
RONCHAM

from United Kingdom

Joined: 31 Mar 2009
Posts: 109
Location: Surrey,
United Kingdom
Thanked: 0 times

PostPosted: Fri Nov 06, 2009 10:54 pm    Post Subject:
Reply with quote Thanks

Hi bengasman, thanks for your input. I meant "regular" boiler as per WB brochure ie not a system or combi boiler. I think the model number 24Ri, 18Ri etc. defines type.

I don't think boiler sizing is an exact science as they always add 10-20% for luck anyway after extensive calculations! But I'm fairly sure 24kw would be overkill and that 15 or 18kw is more than adequate.

My present boiler IS actually working (Ideal RS460) but from previous advice it seems to be possibly close on 20 years old and on borrowed time. On the other hand, I'm told they were made to industrial/commercial spec. back then and tough as old boots.

At risk of raking old ground, I'm also told my system was done on the cheap (with single MV on CH). But I was surprised to find tap stats are £70-80 which is dearer than an extra MV plus normal cylinder stat.
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19164
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Fri Nov 06, 2009 10:55 pm    Post Subject:
Reply with quote Thanks

baxi 105 was known to do it in the north

partscentre where knocking them out at £30 +

which says it all really icon_eek.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Fri Nov 06, 2009 11:01 pm    Post Subject:
Reply with quote Thanks

Did you get my email kev
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 190 times

PostPosted: Sat Nov 07, 2009 9:16 am    Post Subject:
Reply with quote Thanks

RONCHAM wrote:

I don't think boiler sizing is an exact science


It most certainly is not. If nothing else, depending on conditions most rads will dissipate between 10% more and 30% less than the figure given in the tables

RONCHAM wrote:

15 or 18kw is more than adequate.


Like I said, add up the lenght of all the radiator panels and you will get the output in kiloWatts.
RONCHAM wrote:

My present boiler IS actually working (Ideal RS460) but from previous advice it seems to be possibly close on 20 years old and on borrowed time.


Those old lumps have pro's and cons. There is nothing in them, so little to go wrong, bit like a vw beetle. The performance is terrible, bit like a vw beetle.

RONCHAM wrote:

On the other hand, I'm told they were made to industrial/commercial spec.


It is purely due to simplicity.

__________________
Don't feed the troll.
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 190 times

PostPosted: Sat Nov 07, 2009 9:23 am    Post Subject:
Reply with quote Thanks

doitall wrote:
Pretty sure the pin holing plates are something to do with domestic water quality/type so could well be regional.

icon_eek.gif
If it rots through stainless steel, what will it do to me? icon_eek.gif icon_eek.gif

How did you come to the conclusion that it is in the domestic side and not in the system side?

__________________
Don't feed the troll.
Back to top
 Alert Moderators
RONCHAM

from United Kingdom

Joined: 31 Mar 2009
Posts: 109
Location: Surrey,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 07, 2009 11:16 am    Post Subject:
Reply with quote Thanks

Hi bengasman, that's a good approx. you gave on radiator output/boiler sizing. I checked against Stelrad figures and it gives their quoted outputs plus about 10% (which is probably a good thing?). And suggests my living room rads are giving out about 4kw (but I suspect less) against a calculated requirement of about 2.5kw.

I'd like to think I can change/upsize a rad if desirable and boiler has adequate capacity, even if it attracts accusations from Goldberg of fiddling!!

My Drayton TRVs are at least 10 years old and I'm wondering if I should use the opportunity when the system is drained to get them changed as a matter of course??
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Sat Nov 07, 2009 11:23 am    Post Subject:
Reply with quote Thanks

If they are TRV 4 then they seem very reliable and I would not bother to change them.

Think carefull about what you will achieve by changing rads.

I have not read all but you seem to be sayingthe room needs 2.5 kW but you already have 4 kW of rads ???

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
RONCHAM

from United Kingdom

Joined: 31 Mar 2009
Posts: 109
Location: Surrey,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 07, 2009 11:34 am    Post Subject:
Reply with quote Thanks

Thanks Agile.

Main task is a new boiler and upgrading controls. I'm quite happy to keep exisiting rads (provided they don't leak with all the new power surging thru them!). Just thought, for completeness, might be a good time to change TRVs - would obviously be cheaper whilst guys are on site and system is empty, although still a few hundred pounds.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Sat Nov 07, 2009 11:43 am    Post Subject:
Reply with quote Thanks

RONCHAM wrote:
Thanks Agile.

Main task is a new boiler and upgrading controls. I'm quite happy to keep exisiting rads (provided they don't leak with all the new power surging thru them!). Just thought, for completeness, might be a good time to change TRVs - would obviously be cheaper whilst guys are on site and system is empty, although still a few hundred pounds.


We charge £35 eact to fit TRV 4s to an existing system if replacing the boiler.

Otherwise £60 to drain and refill plus £35 each for fitting TRVs to an existing system.

We dont do any work above cream colour carpets!

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page Previous  1, 2, 3  Next
Page 2 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
What size boiler 19 1020 Sun Jun 03, 2007 2:42 pm
New boiler and gas pipe size 9 560 Mon Jun 04, 2007 6:50 pm
Boiler size 3 300 Sat Jan 26, 2008 7:07 pm
pipework size for replacment boiler. 6 420 Fri Nov 17, 2006 10:55 am
What size boiler 4 140 Tue Nov 03, 2009 6:11 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.