Downlights Issues - Fire rating/Insulation/LED/Efficiency


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
BuildingNovice

from United Kingdom

Joined: 03 Mar 2010
Posts: 90
Location: Aberdeen,
United Kingdom

PostPosted: Sun Apr 18, 2010 10:30 am Reply with quote

I have new single storey kitchen extension with a V shaped pitched ceiling and roof, which has a 150mm void, and want to install some downlights.

Please could someone confirm whether I need a fire-rated downlight (i.e. I am not sure if a ceiling/roof in my scenario, which does not have a living space above it, is covered by the regulations). I could not find the relevant section in the part B regulations booklet.

Irrespective of the above, is it OK to lay insulation around the downlight, or must this be cut back, or should an insulation guard be fitted. I will probably go for the aluminium reflector type to avoid heat being sent to the rear.

I know LED downlights can solve the heat issue, but I have read they do not give sufficient light? Would be interested to hear from anyone who has these installed.

Lastly, are the energy efficiency requirements that 1 in 4 lights need to be EE or 1 light per 25mm2 area, or do both these criteria have to be met? My extension is 50mm2 and so do I just need 2 EE lights, even though I will probably have 20 lights in total.

Is there a good guide on the above on the net somewhere?

Many thanks
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
flameport

from United Kingdom

Joined: 10 Mar 2007
Posts: 4154
Location: Bournemouth,
United Kingdom
Thanked: 664 times

PostPosted: Sun Apr 18, 2010 1:56 pm Reply with quote

BuildingNovice wrote:
I have new single storey kitchen extension with a V shaped pitched ceiling and roof, which has a 150mm void, and want to install some downlights.

There is no way any halogen downlights can be installed there, and still be compliant with building regulations.
The void will need to be insulated, and all halogen downlighters require clear space above them - typically at least 150mm, sometimes more.

Cutting holes in the insulation is no good, since the insulation is required.
Covering the downlighters with insulation is no good either, since they will overheat and either cease working, cause a fire, or both.
Back to top
The following user says thank you to flameport for this useful post:
BuildingNovice (18 Apr 2010)
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 15946
Location: Yorkshire,
United Kingdom
Thanked: 221 times

PostPosted: Sun Apr 18, 2010 2:21 pm Reply with quote

Back to top
The following user says thank you to Steve for this useful post:
BuildingNovice (18 Apr 2010)
 Alert Moderators
BuildingNovice

from United Kingdom

Joined: 03 Mar 2010
Posts: 90
Location: Aberdeen,
United Kingdom

PostPosted: Sun Apr 18, 2010 2:39 pm Reply with quote

Would LED lights solve the (heating) problem?

Would covering an LED light with insulation be OK?

But not sure how good the lighting effect is.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 15946
Location: Yorkshire,
United Kingdom
Thanked: 221 times

PostPosted: Sun Apr 18, 2010 2:49 pm Reply with quote

BuildingNovice wrote:
Would LED lights solve the (heating) problem?

Would covering an LED light with insulation be OK?

But not sure how good the lighting effect is.

To a degree.

Not sure.

OK for feature lighting, not that great for ambient lighting. (Just like halogen spots really)
Back to top
 Alert Moderators
BuildingNovice

from United Kingdom

Joined: 03 Mar 2010
Posts: 90
Location: Aberdeen,
United Kingdom

PostPosted: Sun Apr 18, 2010 3:02 pm Reply with quote

Thanks Steve

Lights are really mainly 'task' lighting for a kitchen, so will explore LED option if that's the only way to get recessed lights in this scenario.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 15946
Location: Yorkshire,
United Kingdom
Thanked: 221 times

PostPosted: Sun Apr 18, 2010 3:28 pm Reply with quote

Create a false ceiling?
Back to top
 Alert Moderators
BuildingNovice

from United Kingdom

Joined: 03 Mar 2010
Posts: 90
Location: Aberdeen,
United Kingdom

PostPosted: Sun Apr 18, 2010 3:36 pm Reply with quote

Good idea, but unfortunately don't have the height for a false ceiling
Back to top
 Alert Moderators
ericmark

from United Kingdom

Joined: 27 Jan 2008
Posts: 7644
Location: Flintshire,
United Kingdom
Thanked: 647 times

PostPosted: Sun Apr 18, 2010 4:54 pm Reply with quote

Discharge lighting will solve heat problem although with 50mm lamps they can take with GU10 fittings tungsten, discharge or LED and one would need to do something to stop tungsten being fitted. With 150mm down lights discharge fittings can be used so no mistakes can be made latter. The other option is pods where the lights stick out of the ceiling.

The 50mm lamps have a very narrow angle and getting general lighting with such a small angle means the ceiling will look like a planetarium and although they do help the look of the room they seem to give out less light than a TocH candle so really it needs discharge lighting which could be supplemented with 50mm units rather then rely on just 50mm units.

Using low voltage rather than extra low voltage fitting does allow the use of discharge units, that is florescent or cold cathode which are better than LED units but the lamps are often longer than the tungsten versions and you have to be very careful with selection so they can take extra depth.

The 150mm units can use either lamps designed to replace the tungsten bulb or the 2D types both have many sizes but one can fit 28W and compared with the 11W of the 50mm units they seem to give 3 or 4 times the light output mainly because of spread pattern.

With a V shaped ceiling I would think florescent tubes in the apex with white panel below to reflect the light as seen in many airports would give light without being seen.

If the florescent is going to be hard to access using HF type will give a lot longer life and one should not have to touch them for 5 years. Of course no guarantee but we used them over machines both as no stroboscopic effect and low maintenance.
Back to top
The following user says thank you to ericmark for this useful post:
BuildingNovice (18 Apr 2010)
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Swap tubes for compact fluorescents for better efficiency? 4 460 Thu Oct 30, 2008 2:02 pm
underfloor heating efficiency 7 600 Mon Apr 11, 2005 3:21 pm
High efficiency warehouse lighting 13 700 Sat Feb 14, 2009 4:10 pm
Electric Heating Efficiency 5 580 Thu Sep 06, 2007 9:02 am
Weired Energy efficiency bulb problem 13 480 Tue Jun 09, 2009 9:03 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.