ajrobb

from United Kingdom

Joined: 23 Jan 2010
Posts: 1656
Location: Sussex,
United Kingdom
Thanked: 162 times

PostPosted: Sun Jan 02, 2011 7:58 am Reply with quote


Should I consider getting a magnaclean filter installed on my fragile dual Keston Celsius 25 system? If so, where? As it is primarily to protect the boilers, my initial thought is it should be in the low-loss header between the primary return and the boilers, maybe on the far right of the picture, next to the gas meter, so it is immediately before the boiler returns.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
twgas

from United Kingdom

Joined: 26 Oct 2007
Posts: 4776
Location: Kent,
United Kingdom
Thanked: 406 times

PostPosted: Sun Jan 02, 2011 8:30 am Reply with quote

I would say yes, to near the gas meter.
Back to top
 Alert Moderators
sherbert

from United Kingdom

Joined: 13 Jul 2007
Posts: 320
Location: Sussex,
United Kingdom
Thanked: 52 times

PostPosted: Sun Jan 02, 2011 8:32 am Reply with quote

Yes ....

That would be fine

Also consider fitting the dual magnaclean that has a stariner built into it as well
Back to top
 Alert Moderators
GaytonTonner

from United Kingdom

Joined: 14 Nov 2010
Posts: 189
Location: Manchester,
United Kingdom
Thanked: 3 times

PostPosted: Sun Jan 02, 2011 9:26 am Reply with quote

Do not fit the Magnaclean or the Fernox as they have plastic bodies. The pipe lugs on Magnacleans regularly rip off when the lid is taken off. It happened with me. Luckily the filter had two proper full-bore isolating valves, rather than the Mickey Mouse valves they supply.

Fit a brass Magnabooster. A bit more expensive, but the best. It will be insurance for the two boiler setup. Initially clean the filter every week, then every month then once a year. You will be amazed at how much magnentite they pick up. The Magnabooster is very easy to flush out.
Back to top
 Alert Moderators
simond

from United Kingdom

Joined: 26 Oct 2004
Posts: 4071
Location: Surrey,
United Kingdom
Thanked: 273 times

PostPosted: Sun Jan 02, 2011 11:02 am Reply with quote

Excellent advice from GT.

The Magnacleans could rival the Kestons for reliability.

My question would be, why bother fitting a filter to a Keston? It is guilding a turd, surely? Why not wait till they go in the skip and fit one then?
Back to top
 Alert Moderators
GaytonTonner

from United Kingdom

Joined: 14 Nov 2010
Posts: 189
Location: Manchester,
United Kingdom
Thanked: 3 times

PostPosted: Sun Jan 02, 2011 11:15 am Reply with quote

simond wrote:
Excellent advice from GT.

The Magnacleans could rival the Kestons for reliability.

My question would be, why bother fitting a filter to a Keston? It is guilding a turd, surely? Why not wait till they go in the skip and fit one then?


Over 10 years ago Kestons were excellent quality. The condensing boiler they made with no electronic board and a a spiral heat exchanger with a top mounted burner (I think they were the first to do this) was superb and worked brilliantly on thermal stores. The boiler was simple and effective. It cycled like hell on direct systems, of which Keston said did not harm the boiler, but sung on a thermal store with two anti-cycle thermostats. I know of a few that are approx 15 years old and have never gone wrong at all. They are simple to fix with not much in them.

They then started to make complicated boilers to compete with Vaillant et al, and sell to the mass market. Their reputation suffered greatly. The quality went down with take-overs.

I believe the quality is picking up.
Back to top
 Alert Moderators
Andygasman2010

from United Kingdom

Joined: 03 Mar 2010
Posts: 2176
Location: Middlesbrough,
United Kingdom
Thanked: 202 times

PostPosted: Sun Jan 02, 2011 11:57 am Reply with quote

I've seen this pic before... Is it your boiler?
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4900
Location: Suffolk,
United Kingdom
Thanked: 910 times

PostPosted: Sun Jan 02, 2011 2:59 pm Reply with quote

I would fit the Debris cleaner in the Return pipe to the left of the Expansion vessel in your pic, this way it would protect both boilers without compromising the low loss header! icon_wink.gif
Back to top
 Alert Moderators
ajrobb

from United Kingdom

Joined: 23 Jan 2010
Posts: 1656
Location: Sussex,
United Kingdom
Thanked: 162 times

PostPosted: Sun Jan 02, 2011 3:39 pm Reply with quote

Andygasman2010 wrote:
Is it your boiler?

Sadly, they are. I tried in an earlier post to get them condensing AND heating DHW but I've given up; I couldn't get the boiler return to stay much below 60C without taking the flow in the LLH too low. At least I don't have frozen condensate problems. icon_confused.gif

The Kestons only have a single flow and return each. I guess that makes them 'heat only' boilers. Do 'system' boilers generally support 4-pipe installations with separate DHW and CH temperatures?
Back to top
 Alert Moderators
ajrobb

from United Kingdom

Joined: 23 Jan 2010
Posts: 1656
Location: Sussex,
United Kingdom
Thanked: 162 times

PostPosted: Sun Jan 02, 2011 4:02 pm Reply with quote

Boilerman2 wrote:
I would fit the Debris cleaner in the Return pipe to the left of the Expansion vessel in your pic, this way it would protect both boilers without compromising the low loss header! icon_wink.gif

I understand that the flow in the LLH is needed to protect the heat exchangers from cracking again (2 so far). I've already opened the gate valve wide to maximise LLH flow. So, are you recommending putting the filter in the primary circuit return to keep the LLH unrestricted?

In car engines, they used to have by-pass oil filters that were much finer than full-flow filters. These kept the oil cleaner before modern detergents as they could use the full pressure of the pump, but didn't offer 100% protection from larger particles. Are all central heating filters designed only for full flow or are some put into a by-pass?
Back to top
 Alert Moderators
GaytonTonner

from United Kingdom

Joined: 14 Nov 2010
Posts: 189
Location: Manchester,
United Kingdom
Thanked: 3 times

PostPosted: Sun Jan 02, 2011 4:08 pm Reply with quote

ajrobb wrote:
Andygasman2010 wrote:
Is it your boiler?

Sadly, they are. I tried in an earlier post to get them condensing AND heating DHW but I've given up; I couldn't get the boiler return to stay much below 60C without taking the flow in the LLH too low. At least I don't have frozen condensate problems. icon_confused.gif

The Kestons only have a single flow and return each. I guess that makes them 'heat only' boilers. Do 'system' boilers generally support 4-pipe installations with separate DHW and CH temperatures?


The coil in the cylinder could be too small. Condensing Performance could be improved by using a plate heat exchanger, that takes both boiler's outputs and some more. That way the return temperature would be low from the cylinder with the DHW cylinder reheating very quick, meaning you could downsize the cylinder saving money.

You could have a blending valve in the return from the cylinder set to say, 50-55C. This way the return will be under the dew point most of the time heat DHW.

Did you write you had 2 cracked heat exchangers on the Kestons? Then I would use a blending valve on the return to the boilers, this ensures the temperature is not too low on a cold start and keeps the condensing efficiency high.

How are you sequencing the boilers?
Back to top
 Alert Moderators
snb

from United Kingdom

Joined: 10 Oct 2007
Posts: 1525
Location: Norfolk,
United Kingdom
Thanked: 231 times

PostPosted: Sun Jan 02, 2011 4:12 pm Reply with quote

not sure your crude version of a low loss header is of much use. I think you would have much more luck with lower return temps with purpose made version.

I'm sure more experienced commercial guys on here would have some thoughts
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18839
Location: Bath,
United Kingdom
Thanked: 1515 times

PostPosted: Sun Jan 02, 2011 4:22 pm Reply with quote

It will need to go in the common return to the left of the expansion vessel.

Sorry boilerman didn't read your post till after I posted. icon_wink.gif
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18839
Location: Bath,
United Kingdom
Thanked: 1515 times

PostPosted: Sun Jan 02, 2011 4:25 pm Reply with quote

snb wrote:
not sure your crude version of a low loss header is of much use. I think you would have much more luck with lower return temps with purpose made version.

I'm sure more experienced commercial guys on here would have some thoughts


It isn't a header snb.

A simple straight forward reverse return set up icon_wink.gif
Back to top
The following user says thank you to doitall for this useful post:
ajrobb (5 Jan 2011)
 Alert Moderators
ajrobb

from United Kingdom

Joined: 23 Jan 2010
Posts: 1656
Location: Sussex,
United Kingdom
Thanked: 162 times

PostPosted: Sun Jan 02, 2011 4:28 pm Reply with quote

GaytonTonner wrote:
The coil in the cylinder could be too small.

The 300l cylinder can take the full output of both boilers, at least when cool. However, I need to keep the boiler flow above 65C to heat the DHW above 60C and trigger the cylinder thermostat. I have tried partially closing the LLH gate valve to increase the temperature rise across the boiler to 20C at full load. Unfortunately, at part load, the temperature rise drops away to about 6C at 'cruising' load. I'm nervous about pushing up the temperature rise across the boilers as I've already had 2 heat exchangers replaced. I notice that the first boiler to come off full load drops its pump speed. I'm worried that having any restriction in the LLH will allow flow to reverse (or at least slow way down) if one boiler's pump is pushing harder than the other.

I'd wondered about a temperature limiting mixer instead of the gate valve to keep the boiler return at 45C and set the feed to 65C. I decided against that as it is easy to increase the feed above 65C. I'd also want to replace the knobs with pre-sets. This would limit heating in cold weather... Is there a mixer that allows a fixed temperature rise in a LLH?

Quote:
You could have a blending valve in the return from the cylinder set to say, 50-55C. This way the return will be under the dew point most of the time heat DHW.

I don't see how that would affect the temperature in the LLH.

Quote:
How are you sequencing the boilers?

I currently run the CH 24x7 with a programmable room thermostat. The DHW I have on for an hour in the early morning before the CH and again in the afternoon. The secondary DHW circulation (bronze pump) wastes a lot of heat.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2, 3, 4, 5, 6, 7, 8, 9  Next
Page 1 of 9

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
magnaclean filter/scale reducer? Necessary? 8 160 Sat May 12, 2012 8:29 am
Powerflush and magnaclean filter 33 11940 Thu Aug 30, 2007 9:24 am
Dosing Sytem Through Magnaclean Filter 3 160 Sat Nov 13, 2010 10:55 am
Sentinel Magnetite System Filter Vs Magnaclean 15 5480 Mon Sep 28, 2009 10:58 pm
Is Magnaclean filter required after a Powerflush? 10 1680 Thu Jan 03, 2008 5:09 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.