Hello folks.
I went to see an install the other day:
A standard 60A 6 way Wylex board feeding a 4 way garage sub board at 45A and an adjacent 6 way 60A Wylex board in turn feeding (amongst other circuits) a 45A cooker circuit.
All 45A circuits are fed in 6mm2 T&E.
Yuk!
So I'm quoting for a clean-up: I'm installing one CU to replace the two 6 ways.
But what would you do with the sub main to the 4 way in the garage?
It currently feeds a 30A circuit, a 20A circuit and 2 5A circuits.
Would you:
Feed it from the main board?
Run a separate sub board from henley blocks to feed it?
Or extend the tails back to the main board (on the other side of the wall)?
If the first two, how would you satisfy discrimination? |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
ricicle

Joined: 14 Sep 2006 Posts: 6080 Location: Gloucestershire, United Kingdom Thanked: 348 times
|
Posted: Tue Feb 08, 2011 10:46 pm |
|
|
You will struggle to provide any discrimination between MCBs in a sub-board and an MCB feeding the sub-board in a short-circuit condition or possibly from inrush if any welding equipment were to be used in the garage.
You might be better feeding via henleys with a switch-fuse although that depends on your interpretation of the single point of isolation regulation for the whole installation. |
|
| Back to top |
|
|
|
 |
dannyboi2003

Joined: 11 Jul 2006 Posts: 482 Location: West Glamorgan, United Kingdom Thanked: 14 times
|
Posted: Wed Feb 09, 2011 9:15 am |
|
|
Are the cartridge fuse holders for consumer units still available, MEM springs to mind? Could you feed it from the main board (non rcd way depending on cable) protected by a fuse to get around the mcb discrimination? |
|
| Back to top |
|
|
|
 |
holmslaw

Joined: 12 Dec 2006 Posts: 5844 Location: Vanuatu Thanked: 400 times
|
Posted: Wed Feb 09, 2011 9:30 am |
|
|
..
Last edited by holmslaw on Mon Apr 09, 2012 7:24 am, edited 1 time in total |
|
| Back to top |
|
|
|
 |
securespark

Joined: 11 Jan 2004 Posts: 22665 Location: Cheshire, United Kingdom Thanked: 317 times
|
Posted: Wed Feb 09, 2011 10:00 am |
|
|
Thanks rice, that's as I thought.
danny, it's a possibility.
holms, that's my preferred route, by far.
The board is in a semi-recessed cupboard in the hall that's too small, but maybe I can persuade the customer to resite or open the cupboard up.
Thanks guys. |
|
| Back to top |
|
|
|
 |
ban-all-sheds

Joined: 27 Aug 2003 Posts: 41736 Location: London, United Kingdom Thanked: 1354 times
|
Posted: Wed Feb 09, 2011 6:13 pm |
|
|
| securespark wrote: | Hello folks.
I went to see an install the other day:
A standard 60A 6 way Wylex board feeding a 4 way garage sub board at 45A and an adjacent 6 way 60A Wylex board in turn feeding (amongst other circuits) a 45A cooker circuit.
All 45A circuits are fed in 6mm2 T&E.
Yuk!
So I'm quoting for a clean-up: I'm installing one CU to replace the two 6 ways.
But what would you do with the sub main to the 4 way in the garage?
It currently feeds a 30A circuit, a 20A circuit and 2 5A circuits.
Would you:
Feed it from the main board?
Run a separate sub board from henley blocks to feed it?
Or extend the tails back to the main board (on the other side of the wall)? |
|
|
| Back to top |
|
|
|
|
|
 |
holmslaw

Joined: 12 Dec 2006 Posts: 5844 Location: Vanuatu Thanked: 400 times
|
Posted: Wed Feb 09, 2011 7:46 pm |
|
|
..
Last edited by holmslaw on Mon Apr 09, 2012 7:24 am, edited 1 time in total |
|
| Back to top |
|
|
|
 |
sparkiedave

Joined: 01 Jan 2009 Posts: 231 Location: Gwynedd, United Kingdom Thanked: 12 times
|
Posted: Wed Feb 09, 2011 8:31 pm |
|
|
one isolator, henley blocks then tails to each board would be my preferred option, if something is tripped in the garage there's no effect on house wiring, and no need to go into the house to re-set a breaker/RCD
Last edited by sparkiedave on Wed Feb 09, 2011 8:37 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
sparkiedave

Joined: 01 Jan 2009 Posts: 231 Location: Gwynedd, United Kingdom Thanked: 12 times
|
Posted: Wed Feb 09, 2011 8:33 pm |
|
|
with a fuse on tails to garage depending on cable type |
|
| Back to top |
|
|
|
 |
ban-all-sheds

Joined: 27 Aug 2003 Posts: 41736 Location: London, United Kingdom Thanked: 1354 times
|
Posted: Thu Feb 10, 2011 1:16 am |
|
|
The original question was badly worded. As it included "If the first two, how would you satisfy discrimination?" I took it to mean that the 3rd option had no discrimination issues because it was describing extending the tails to the board in the garage, on the other side of the wall. |
|
| Back to top |
|
|
|
 |
mfarrow

Joined: 02 Nov 2009 Posts: 752 Location: Warwickshire, United Kingdom Thanked: 72 times
|
Posted: Thu Feb 10, 2011 8:06 am |
|
|
| dannyboi2003 wrote: | | Are the cartridge fuse holders for consumer units still available, MEM springs to mind? |
Not sure whether the new Memera 3 stuff will work in their domestic boards (???). Otherwise I believe they're still in Wylex's catalog, hager up to a certain size (32A I think) and of course the industrial sets like Merlin Gerin will work if a little pricier.
The usual problem is that manufacturer's data states you can't pull fuses to isolate circuits live, so you will either have to knock the whole lot off when you want to work on the sub board or install a separate isolator in the board just for that fuse/circuit. |
|
| Back to top |
|
|
|
 |
ban-all-sheds

Joined: 27 Aug 2003 Posts: 41736 Location: London, United Kingdom Thanked: 1354 times
|
Posted: Thu Feb 10, 2011 8:40 am |
|
|
I've noticed as well that sometimes even within the same make, fuse carriers and MCBs have the feed tunnels in different places making mix'n'match on a busbar a little tricky... |
|