have a 3 bedroom extension going onto the side of my 1940's bungalow.
The wiring within these bedrooms will be extensions of the existing circuits and will not require any tampering of the main board.
Regardless of my qualifications, If I wish to do this work myself, I am entirely within the rules todo so??
Please note how carefully I have disguised this topic, because I know how sick to death you spark's are about answering part p related questions.
I think it would be foolish to extend the original circuits. How old is that wiring?
I would strongly recommend new circuits for the extension - if you are competent that you will do a good job, building control will not have any issues when they come to inspect your work!
Dont forget that you should also upgrade the main equipotential bonding, and install supplymentary equipotential bonding to any rooms containing a bath or shower in the extension. You will also be required to protect the new sockets with a 30mA RCD for supplymentary protection - I doubt your existing sockets have this, unless you have had a new CU installed?
In my experience, properties your age will likely have an old re-wireable CU, and an ELCB, with an earth rod which has been forgoten about, lost, broken, ripped out. Subsequently, no earthing to the house. You should also get this checked!
Bear in mind that your extension will have more value, and be easier to sell, if you have an EIC cert for the installation.
Are you having the extension built for you? Are you prepared to work around the builders when installing your own lecky? You find them hard to work with, time scale wise.
On top of the issues mentioned by Lectrician, how do you know that you've not already gone wrong with that decision?
With the socket circuits, what type are they? What floor area do they already serve? Will the additional floor area be OK?
For all of the circuits that you extend, what will the new R1+R2 be, and will they meet the disconnection time given the type of protective devices you have?
You've made a design decision which might be unsupportable in practice.
You should get yourself up to speed on issues like this, and all the other regulations that will apply - get hold of these (apologies if you're already at the stage where you don't need the first one).
IMPORTANT NOTE - when buying books from Amazon, seek confirmation that they are the latest versions.
http://www.amazon.co.uk/exec/obidos/ASIN/0852028172
http://www.amazon.co.uk/exec/obidos/ASIN/0863413749
or http://www.iee.org/Publish/Books/WireAssoc/index.cfm?book=WR 261
http://www.iee.org/Publish/Books/WireAssoc/index.cfm?book=WR 500
http://www.amazon.co.uk/exec/obidos/ASIN/0953788539
or http://www.tlc-direct.co.uk/Main_Index/Electricians_Guide_Book/index.html
http://www.iee.org/Publish/Books/WireAssoc/index.cfm?book=WR 250
Also, not essential, but although the Electricians Guide shown above is a good explanation of the regs, if you fancy one with a bit more of the electrical engineering theory behind it all, I can recommend this in addition:
http://www.iee.org/Publish/Books/WireAssoc/index.cfm?book=NS 031
DIY Electrical work and the law
On January 1st 2005 legislation came into effect which brought electrical work in dwellings under the Building Regulations, and made it a controlled service. This amendment to the Building Regulations, known as "Part P", imposes safety requirements, and also classifies electrical installation work into two basic categories, notifiable and non-notifiable.
Essentially the distinction is between major work, or work in what are deemed high-risk areas such as kitchens, bathrooms and gardens, and minor work such as replacing switches or adding sockets to existing circuits. (NB to those with a knowledge of the IEE Wiring Regulations, the term "minor work" is used here in its generic sense rather than the meaning defined in the Wiring Regs.)
A very important and fundamental point to note is that DIY electrical work has not been outlawed. It has been brought within the remit of the Building Regulations and cannot be carried out as freely as it was before, and in many cases cannot be carried out without involving your local council, but you may still DIY.
Major work is classed as notifiable, i.e. it must be notified to your Local Authority's Building Control department (LABC). How this happens depends on who does it.
If the work is carried out by an electrician who is registered with one of the organisations who administer self-certification schemes, (sometimes referred to as "Competent Person" schemes) they carry out the work and report the details to their scheme organiser, who then notify the appropriate LABC that the work has taken place, and that it has been certified by the person who carried it out as being in compliance with the Building Regulations. You may be familiar with this method of operation if you have ever had windows replaced by a FENSA member.
If the work is carried out by someone who is not registered with one of the schemes, be they an electrician or another type of tradesman (e.g. kitchen fitter) who has chosen not to register, or a DIYer, then it must be notified to LABC in advance in the same way that any building work which requires their involvement is notified in advance. And just like when you are building an extension, or converting a loft, etc, there is a fee payable to LABC to cover their activities related to checking compliance with the Building Regulations. (But see "LABC Issues" below regarding this).
Another important point to note is that apart from a Building Inspector, nobody can certify someone else's work as being compliant with the Building Regulations. Unless arranged by or in cooperation with LABC, a 3rd party electrical inspection is of no value in terms of complying with the law.
The full text of the legislation can be found here: http://www.opsi.gov.uk/si/si2004/20043210.htm and it is worth making the effort to read it, and understand it, because there is a lot of misinformation on the Internet, some of it put out by organisations with a vested interest in pretending that DIY work is illegal, some of it by LABCs who have either misunderstood the legislation, or who are also attempting to mislead the public in order to reduce the amount of work notified to them by non-self-certifying people, some of it, surprisingly, by the ODPM themselves (The Office of the Deputy Prime Minister were responsible for the legislation), and much of it on electrical advice and discussion fora like this one.
At the time of writing (September 2005), the following work was classed as not needing notification to LABC:
[code:1]1. Work consisting of -
(a) replacing any socket-outlet, control switch or ceiling
rose;
(b) replacing a damaged cable for a single circuit only;
(c) re-fixing or replacing enclosures of existing
installation components, where the circuit
protective measures are unaffected;
(d) providing mechanical protection to an existing
fixed installation, where the circuit protective
measures and current carrying capacity of
conductors are unaffected by the increased thermal
insulation.
2. Work which -
(a) is not in a kitchen, or a special location,
(b) does not involve work on a special installation, and
(c) consists of -
(i) adding light fittings and switches to an
existing circuit;
(ii) adding socket outlets and fused spurs to an
existing ring or radial circuit; or
(iii) installing or upgrading main or supplementary
equipotential bonding.
3. Work on -
(a) telephone wiring or extra-low voltage wiring for the
purposes of communications, information technology,
signalling, control and similar purposes, where the
wiring is not in a special location;
(b) equipment associated with the wiring referred to in
sub-paragraph (a).
[/code:1]
The terms "kitchen", "special installation" and "special location" are defined in the legislation.
Like any law, things can change, and you are urged to ensure that you make yourself familiar with the law as it stands now, not necessarily as it was when this document was written.
The starting point on the ODPM website for information related to Building Regulations is http://www.odpm.gov.uk/stellent/gro...ments/sectionhomepage/odpm_buildreg_page.hcsp and a list of the relevant legislation can be found at http://www.odpm.gov.uk/stellent/groups/odpm_buildreg/documents/page/odpm_breg_600270.hcsp .
It is in the nature of the Internet for sites to change, and it may well be that today, when you are reading this, the links above no longer work, and you will have to search for the pages you want.
Useful Information
On the ODPM website there are a number of "Approved Documents"
( http://www.odpm.gov.uk/stellent/groups/odpm_buildreg/documents/divisionhomepage/br0041.hcsp ). These are not definitions of the law, nor do they tell you what you must, or must not, do. Instead they give guidance on ways in which the law can be satisfied. They do point out that you are not obliged to adopt any solution contained in them if you prefer to meet the requirements in another way, but that said they are useful as they contain common sense advice and often there is no good reason not to adopt the solutions they contain.
Approved Document P can be found here: http://www.odpm.gov.uk/stellent/groups/odpm_buildreg/documents/page/odpm_breg_br1007.pdf .
Technical Requirements
The technical requirements laid down by Part P are remarkably simple. They are:
  1. Reasonable provision shall be made in the design, installation, inspection and testing of electrical installations in order to protect persons from fire or injury.
  2. Sufficient information shall be provided so that persons wishing to operate, maintain or alter an electrical installation can do so with reasonable safety.
It is worth noting however that they apply to all work, not just notifiable work, no matter who does it. So a DIYer adding a socket or a fused spur to a ring final circuit must work to the same technical standards as a registered electrician doing a complete rewire.
The biggest practical issue that arises is testing. To carry out testing of electrical circuits requires expertise and equipment, neither of which are likely to possessed by the average DIYer. So although Part P allows a DIYer to replace an entire circuit cable if it is damaged, without notification, it is arguable that he could not be sure that he had done it properly unless he carried out a series of tests on it, something he would probably be unable to do.
The IEE Wiring Regulations, aka BS 7671
Surprisingly, perhaps, Part P does not alter the status of the Wiring Regulations. They are still non-statutory, and there is still no legal requirement to adhere to them in domestic installations. This is a source of great discomfort to many electricians, and some of them will jump through hoops to try and prove that they are mandatory, but the fact remains that they are not.
HOWEVER, adherence to them is a very good way of ensuring that you meet the technical requirements of Part P, and you would need a very good reason, and a very good understanding of what you were doing, to decide to not adhere to them.
LABC Issues
As mentioned above, some LABCs are spreading misinformation, either by accident or design, about the status and acceptability of electrical work done by DIYers or other non-registered people.
These include:
1) Stating that such persons simply cannot carry out notifiable work, and that it must be done by registered electricians. The legislation referenced above, Statutory Instrument 2004 No. 3210 The Building (Amendment) (No.3) Regulations 2004 makes it quite clear that this is not the case. LABCs are not allowed to refuse to process Building Notices submitted by non-registered people.
2) Stating that work carried out by a non-registered person must be inspected and tested by someone who is registered, or who they regard as qualified. Again, there is no mention of this requirement in the statutory instrument.
Recently the ODPM issued a circular to local authorities making it absolutely clear that they are not allowed to do this:
http://www.odpm.gov.uk/index.asp?id=1131042
Unfortunately, many LABCs are simply ignoring what the ODPM say, and persisting with their policy of requiring DIYers or other non-registered people to hire someone to inspect and test the work. The ODPM's position on this appears to be that if you are being told this by your LABC you should take them to court.
3) Attempting to impose extra charges to cover the inspection and testing of work done by a non-registered person. An LABC may well elect to subcontract inspection and testing if they do not have the capacity to do it themselves, but they are not allowed to charge extra because of this – the cost to them of subcontracting must be borne by them
Individual local authorities co-ordinate their services regionally and nationally (and provide a range of national approval schemes) via LABC Services. (http://www.labc-services.co.uk).
I recently posed LABC services the following question:
"My local Building Control dept has told me that because of staffing problems they are unable to inspect some building work, and will have to sub-contract it, and that I will therefore have to pay this cost on top of their fees.
Are they allowed to do this?
Their reply was:
"Building Regulation fees are set to a scale that embraces the whole scope of what may be necessary in respect of checking and approving the plans and inspecting the work. The input necessary can vary according to the circumstances of a specific scheme, but the fees are not variable due to this feature.
The local authority has a legal duty to carry out the Building Regulation function to a proper degree. This can also vary in extent according to the demands of any scheme and considerable discretion rests with the authority. However they are responsible to give a proper service within the fee and cannot charge extra for the reason you mention. Indeed if they failed to inspect yet still charged you might have a case for a refund
Note that in your case the problem described above about how LABCs are insisting on EICs issued by qualified electricians might be an issue given that you'll need their cooperation and you'll need the completion certificate, particularly if you decide to play hardball and insist that they do what they are supposed to.
I'm not a spark either, so I'm not being all precious about this.
Yep I've got a copy of electricians guide to the building regs well worth getting.
ban are you saying that if a diyer does some work and calls in LBC then LBC have a duty to inspect and test the installation?
No. If a DIY'er notifies LABC first; then does the work, the LABC have a duty to inspect the installation.
As slippyr4 said, he has to tell them first, but yes, they are supposed to test, that's what their fee is for, and it's what the law says.
In practice, many/most/all LABCs don't do what they should, and insist on the DIYer paying for a 3rd party electrician to inspect and test the work, something which the ODPM have told them to stop doing.
thats what i meant. so if i want to fit a cooker circuit then i tell building control, who then come and inspect first fix etc and then when the job is finished i tell them to come out and do all the testing. sounds ok to me!! where can i find this written?i was told by LBC that i would have to do the testing and provide EIC's etc
you are aware you have to pay a fee, aren't you?
oops?......the law doesnt say that does it? i thought that was an interpretation of the law by opdm which differs to that of the guidance ive seen from labc's - so currently stands as one of the arguable points of the legislation
'P1 Reasonable provision shall be made in the design, installation, inspection and testing of electrical installations in order to protect persons from fire or injury.'
Nobody expects the labc to design or install the works so why would they be expected to do the test?
How long would it reasonably take to test say a 3 bed house?