WPD will not mix systems on the same sub. TT is not part oft the the mix.
In saying this, there is loads of TN-S systems pulled over to TN-C-S were cables are rotting.
We have had PME Presented on sites were TN-S is preferred, and been unable to get the supply changed, even though the supply cable would permit (a four core wavecon).
One site was a caravan park, a single sub feeding the park, a harbour office and two houses. To get TN-S, we had to convert the harbour to TN-S too, the houses were ignored, as they were TT, being supplied by long runs of single cores right upto the cut out (separate fuse and N block). Had to negotiate with the harbour to allow this to be done.
In saying this, there is loads of TN-S systems pulled over to TN-C-S were cables are rotting.
We have had PME Presented on sites were TN-S is preferred, and been unable to get the supply changed, even though the supply cable would permit (a four core wavecon).
One site was a caravan park, a single sub feeding the park, a harbour office and two houses. To get TN-S, we had to convert the harbour to TN-S too, the houses were ignored, as they were TT, being supplied by long runs of single cores right upto the cut out (separate fuse and N block). Had to negotiate with the harbour to allow this to be done.