radiators get hot when only hot water selected

j&c

Joined
21 Aug 2006
Messages
2
Reaction score
0
Country
United Kingdom
The tank thermostat and the 3 way valve electrics have been changed but problem still exists. The system is a pumped system and the upstairs rads seem to get hot first :(
 
Sponsored Links
Where is the hot water return? should be last one before boiler.

If that isn;t the problem, and you are sure synchron motor is OK and control signal is OK, and you have watched the position indicator demonstrating that the paddle is moving to the correct position, mechanics of valve might be failing to seal on heating branch; change it.
 
Paul Barker said:
Where is the hot water return? should be last one before boiler.

If that isn;t the problem, and you are sure synchron motor is OK and control signal is OK, and you have watched the position indicator demonstrating that the paddle is moving to the correct position, mechanics of valve might be failing to seal on heating branch; change it.

Thank you it looks as thiugh I have no option except to drain down the system
TY for reply
 