microbore heating

This topic originated from the How to page called Removing a radiator
Click here to return to the page called Removing a radiator.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  Bookmark and Share View previous topic :: View next topic  
Author Message
smokie

from United Kingdom

Joined: 03 Mar 2004
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 03, 2004 10:14 am    Post Subject:
microbore heating
Reply with quote Thanks

I wish to change my Bathroom rad for a heated towel rail. I have a microbore system, is it juat a matter of reduceing the rad outlets to the size of the microbore ??
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
taydo

from United Kingdom

Joined: 27 Jan 2004
Posts: 377
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 03, 2004 10:49 am    Post Subject:
Reply with quote Thanks

yes just buy valves to suit the size of your pipe
Back to top
 Alert Moderators
funkydung

from United Kingdom

Joined: 26 Jan 2004
Posts: 21
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 01, 2004 8:03 am    Post Subject:
Removing a microbore radiator
Reply with quote Thanks

I also have a Microbore system. Does the whole central heating system have to be drained before removing a radiator? Or can you somehow shut off both the "water in" and "water out" valves on the radiator? Seems easy enough to shut off the "water in" valve but the "water out" valve is less obvious. After removing the protective cover there is a nut which seems completely tightened. When you loosen it, water begins to drip out. It seems strange that the nuts are tightened to capacity since surely this suggests that the water is prevented from leaving the rad?

Also, on the microbore system there doesn't appear to be a master drain cock since there is no exposed pipe other than the thin 10mm pipes going into each rad. However, each of the rads on the ground floor seems to have its own drain cock. Should i simply drain down the system through one rad?

Any help greatfully recieved. Many thanks.
Back to top
 Alert Moderators
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4698
Location: Birmingham,
United Kingdom
Thanked: 29 times

PostPosted: Tue Jun 01, 2004 8:22 am    Post Subject:
Reply with quote Thanks

The return pipe shouldn't be fully closed but it may not be far off, it is the lockshield valve for balancing the system. Was that rad working ok?

There are individual drain points because each rad is dropped down on its own individual circuit from the main manifold, so one rad downstairs will drain all the upstairs rads and the drop it is on, but all the other downstairs rads will require draining each drop at a time.
Back to top
 Alert Moderators
funkydung

from United Kingdom

Joined: 26 Jan 2004
Posts: 21
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 01, 2004 8:33 am    Post Subject:
Reply with quote Thanks

Thanks Olski. That makes sense, maybe it wasn't fully closed, just gave that impression. The rad was working fine so maybe it just didn't need to be opened too much. If that is the case, if i were to tighten it completely, would i be able to remove the individual radiator without bleeding the whole system?

I have noticed that there is actually one radiator downstairs without a drain cock. Could it be that this one isn't connected to any other radiators?

Thanks for this help it's a godsend - there's absolutely nothing about removing microbore rads on the net!
Back to top
 Alert Moderators
funkydung

from United Kingdom

Joined: 26 Jan 2004
Posts: 21
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jun 02, 2004 2:05 pm    Post Subject:
Microbore for sure!
Reply with quote Thanks

Sorry to harp on about this. I just want to get this cleared up once and for all.

Can I definitely remove radiators on a microbore system without draining the who C/H system down? (as in by tightening the lockshield and inlet valve).

The only reason im checking this is because a plumber told me that there was absolutely no way id be able to remove any microbore rad without bleeding the system first. Yet other people tell me i can. I'm scared of what might happen!
Back to top
 Alert Moderators
eddy42

from United Kingdom

Joined: 11 Dec 2004
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Dec 11, 2004 12:23 pm    Post Subject:
10mm
Reply with quote Thanks

I recently changed a radiator to a Mere towel rail. The pipe to the rad was 10 mm and I managed to remove the rad without damage to the pipes
just have to be careful as 10 mm bends easy


I have since changed the towel rail feed pipe to 15 mm
Back to top
 Alert Moderators
bathjobby

from United Kingdom

Joined: 06 Oct 2004
Posts: 1062
Location: United Kingdom
Thanked: 2 times

PostPosted: Sun Dec 12, 2004 3:13 pm    Post Subject:
Reply with quote Thanks

If your valves can be closed completely i.e. they are working properly and not knackered, then yes, close the valves and remove the rad. I echo the earlier caution on 10mm copper pipes; they bend and crack VERY easily, do not put any pressure on then. When you are undoing and subsequently tightening the valve connections for removal and refitting, use a tap spanner (or similar, straddled either side of the valve body) to counteract the force you are applying to the valve nut i.e. no force on the pipe; be warned, it WILL break if you let it be the only thing taking the strain of the pressure you use to open / tighten the valve nut.
Also, make sure you are turning the valve nuts the correct way otherwise you may be trying to tighten when attempting to remove and may think they are seized. Remember that the nut is actually part of the radiator fitting and not the valve, if you hadn't sussed this you would be trying to turn it the wrong way.
Back to top
 Alert Moderators
paulmago

from United Kingdom

Joined: 10 Oct 2007
Posts: 18
Location: Leicester,
United Kingdom
Thanked: 0 times

PostPosted: Wed Oct 10, 2007 1:36 pm    Post Subject:
Reply with quote Thanks

i have a downstairs toilet with a micobore radiator and want to change it to a towel rail. i cannot find a drain tap for the system, do i need to drain the whole system if so how? or can i create a trap in some way? or would it be adviseable to freeze the 2 pipes bearing in mind i only have 2 inch of pipe coming out of the wall. any help would be appreciated.
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 21109
Location: Tennessee,
United States of America
Thanked: 574 times

PostPosted: Wed Oct 10, 2007 1:56 pm    Post Subject:
Reply with quote Thanks

err system is ?????

__________________
REMEMBER
last man on the job carry's the can G.S.I.U.R. icon_evil.gif
Back to top
 Alert Moderators
paulmago

from United Kingdom

Joined: 10 Oct 2007
Posts: 18
Location: Leicester,
United Kingdom
Thanked: 0 times

PostPosted: Wed Oct 10, 2007 8:16 pm    Post Subject:
Reply with quote Thanks

My system is an open vent gravity fed.
i am thinking if i lock down both valves on the radiator remove one valve and drain rad , remove rad put a pipe onto both valves open them up and drain?
Back to top
 Alert Moderators
awjenks

from United Kingdom

Joined: 11 Oct 2007
Posts: 2
Location: Coventry,
United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 11, 2007 8:41 am    Post Subject:
Removing a radiator
Reply with quote Thanks

If your system is NOT sealed and has an unsealed central heating cold tank in the loft then this may be of help. Drayton make an item called an Easy Drain Kit.
This kit basically comprises 2 tapering plugs. One of these plugs is used to seal the expansion pipe to the loft tank and the other is used to seal the feed pipe from the loft tank. Now providing only 1 break is made in the system only about an egg-cup full of fluid will escape before a vacuum is created and this prevents further fluid escaping. NOTE that if you just cut a pipe then you have made 2 breaks in the system as BOTH ends of the pipe are open. I have used this gadget to to remove a radiator without having to anything else on numerous occasions.
See the web page below for more info and full instructions on how to use the Drayton Easy Drain Kit htttp://www.invensyscontrolseurope.com/InvensysControlsEurope/en/ProductsServices/Drayton/Ancillariesandspares/
Back to top
 Alert Moderators
paulmago

from United Kingdom

Joined: 10 Oct 2007
Posts: 18
Location: Leicester,
United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 11, 2007 7:59 pm    Post Subject:
Reply with quote Thanks

thanks awjenks, i think what u said makes sense. will check out the kit
Back to top
 Alert Moderators
paulmago

from United Kingdom

Joined: 10 Oct 2007
Posts: 18
Location: Leicester,
United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 11, 2007 8:09 pm    Post Subject:
Reply with quote Thanks

with your method i can block uo pipes as said shut off both present rad valves remove exisisting rad fit towl rad remove one old valve with slight water discharge and fit to new valve on towl rail lock this valve off and open other to fit
Back to top
 Alert Moderators
paulmago

from United Kingdom

Joined: 10 Oct 2007
Posts: 18
Location: Leicester,
United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 11, 2007 8:22 pm    Post Subject:
Reply with quote Thanks

will try to word that better.
block pipes in loft as said, lock down both valves on rad to be removed and seperate from rad, drain rad contents, fit new towl rail, remove one valve from microbore pipe and fit to rail, then lock this valve down, remove the other valve from microbore pipe and fit to towl rail?
Back to top
 Alert Moderators
Display posts from previous:   
  Bookmark and Share View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Microbore heating problems... 4 600 Sun Dec 13, 2009 1:23 pm
Microbore heating systems 12 1380 Wed Jun 08, 2005 9:21 pm
8mm microbore / Central heating 4 320 Fri Dec 18, 2009 7:04 pm
Microbore heating, sludged up? Power flush needed? 12 520 Wed Jan 20, 2010 3:38 pm
Moved to house with Microbore heating - a few questions 2 3940 Fri Mar 03, 2006 12:14 am

JG Speedfit Plastic Pipe Insert 10mm Pack of 50 JG Speedfit Plastic Pipe Insert 10mm Pack of 50£10.87FloPlast Flo-Fit Reducing Tee 15 x 15 x 22mm
FloPlast Flo-Fit Reducing Tee 15 x 15 x 22mm£2.46
Hep20 Flow Rate Calculator Hep20 Flow Rate Calculator£39.97FloPlast Flo-Fit Elbow 10mm Pack of 5
FloPlast Flo-Fit Elbow 10mm Pack of 5£6.92
JG Speedfit Straight Coupler 22mm Pack of 5 JG Speedfit Straight Coupler 22mm Pack of 5£8.90JG Speedfit Stop Cocks 15mm
JG Speedfit Stop Cocks 15mm£5.49



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.