Hi
I am getting a dual fuel cooker, gas hob, electric single oven
total cooker rating from the manual is fairly low at 2055 W
cooker comes with flex and 13Amp plug to plug into a regular kitchen socket in ring circuit
there is a permanent hardwire cooker connector (on its own cooker circuit and 32A MCB at consumer unit) behind the cooker which is currently unused but would be useful to connect the cooker to.
the cooker circuit is controlled by a 45A cooker switch socket (i.e. a cooker switch with an additional plug socket)
Normally plug kettle (3kW) into the socket on the cooker switch socket
total load on the cooker switch socket would be about 22Amps with cooker oven and kettle on at same time
Questions are:
1) Can I lop-off the plug and hardwire the cooker to the hardwire cooker connector using the 3 core 2.5mm flex currently attached to the cooker?
2) what Amp MCB can I safely use bearing in mind I may use a 3kW kettle as well on the cooker switch socket
3) If I use say a 32A MCB in the cooker circuit do I risk a nastly overload of the cooker before it trips if anything goes wrong?
I want the electrician to do as little as needs be. The electrician is a mythical beast working on highly lucrative building jobs and would have to be kidnapped to get any attention.
thanks
I am getting a dual fuel cooker, gas hob, electric single oven
total cooker rating from the manual is fairly low at 2055 W
cooker comes with flex and 13Amp plug to plug into a regular kitchen socket in ring circuit
there is a permanent hardwire cooker connector (on its own cooker circuit and 32A MCB at consumer unit) behind the cooker which is currently unused but would be useful to connect the cooker to.
the cooker circuit is controlled by a 45A cooker switch socket (i.e. a cooker switch with an additional plug socket)
Normally plug kettle (3kW) into the socket on the cooker switch socket
total load on the cooker switch socket would be about 22Amps with cooker oven and kettle on at same time
Questions are:
1) Can I lop-off the plug and hardwire the cooker to the hardwire cooker connector using the 3 core 2.5mm flex currently attached to the cooker?
2) what Amp MCB can I safely use bearing in mind I may use a 3kW kettle as well on the cooker switch socket
3) If I use say a 32A MCB in the cooker circuit do I risk a nastly overload of the cooker before it trips if anything goes wrong?
I want the electrician to do as little as needs be. The electrician is a mythical beast working on highly lucrative building jobs and would have to be kidnapped to get any attention.
thanks